If it's 30ma RCD protected at the origin of the final circuit the maximum permitted Zs is 1667 ohms. If it's not, it's supplying sockets, why isnt it?
Agree with you fully
Definitely can't see into the future, just what I've seen happen over the years, always plays at the back on my mind e.g. FCUs swapped out for sockets, fuses in FCU replaced by screws/wire.
No matter what we try to protect against (perceived or real) something will always be missed, hence evolution of the regs over the years.
Hope that makes sense? Apologies if I've inadvertently offend you, certainly was not my intention.
To add , the live conductors need checking against the formula T= K2 S2/I2 , the resulting number is how long it takes for damage to the live conductors to occur, nothing to do with whether the earth fault loop impedance complies or not.Need to be a little bit careful when applying this.
Yeah, this method then moves the job of earth fault protection from the OCPD to the RCD as the fault current is not enough to operate the OCPD quickly enough. The OCPD will still be covering short circuit protection so this then needs to be checked. If cpc is reduced size then probably ok as the fault current will be higher across live conductors, but you will still need to verify this is satisfactory. If you have situation where cpc is same size as live conductors and it wont satisfy Zs then it also won't satisfy live conductor thermal constraints either as will be the same fault current.
[automerge]1592523436[/automerge]
Seriously mate, I would not worry about what other people do in the future. If they make changes to an electrical installation then they are responsible for them.
Great point.Need to be a little bit careful when applying this.
Yeah, this method then moves the job of earth fault protection from the OCPD to the RCD as the fault current is not enough to operate the OCPD quickly enough. The OCPD will still be covering short circuit protection so this then needs to be checked. If cpc is reduced size then probably ok as the fault current will be higher across live conductors, but you will still need to verify this is satisfactory. If you have situation where cpc is same size as live conductors and it wont satisfy Zs then it also won't satisfy live conductor thermal constraints either as will be the same fault current.
[automerge]1592523436[/automerge]
Seriously mate, I would not worry about what other people do in the future. If they make changes to an electrical installation then they are responsible for them.