I dont see this technique helping.
Lets say the Impedance is 0.02 ohms, at 230 V this equates to 11.5kA.
Now if we introduce an impedance of 0.5 ohms, our circuit is now 0.502 ohms.
At 0.502 ohms standard meters will have a 10% +/- and a 5 digit error +/- around the 0.5 area.
So this equates approx to a +/- of 0.1 ohm, so even with the 0.5 ohm added the reading could be 0.6 ohms or 0.4, a differnace of 0.2 ohm's.
Cheers
So without going into another pointless in depth discussion so you can prove a point, when was the last time you applied the +/- 10% and 5 digit error or so, to any value that you measured with you're MFT/EFI tester, and recorded that amended value on a report sheet??
The above method is just a means of enabling a relatively standard MFT/ELI meter to more accurately measure values that are very close to it's ultimate limit, nothing more, nothing less!!