Hi,
I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything.
Zs was around 3.5 ohms on all of the ring circuits and the oven circuit and lighting circuits were between 3-4.5 ohms.
The Ze was 1.1 ohms and R1+R2 was between 0.9-0.23 ohms at the various points. I bypassed the type AC RCD but still got the same results.
The previous EICR report from Napit also had higher than expected Zs but they only tested for R2 and passed the installation.
I’m not that familiar with TT systems, is this expected / acceptable or was it not property investigated previously, what could be the issue?