We've had a lowest thread how about the highest? obviously scuppered a bit by how high the tester goes but i've had 1147ohms once, terrible ground
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Highest ze on a tt in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
On a 30mA rcd its 1667ohms, 200 is the standard as anything above that is classed as unstable niceic like to see less than 100 thoughJust read on the voltimum site that up to 1660 ohms is acceptable for a TT reading, and it is accepted that over 200 tripping times become unreliable. Will go back to it in a minute but can we discuss this aspect. every one seems to think under 200 is the maximum standard, and me too, have always managed to acheive it so far, thanks to the tips on here.
Hi
Dontbe confused by max Ra (rod resistance), 200ohms as suggested in BS 7671 and, max permitted Zs when a circuit is protected by a 30mARCD = 1667ohms.
Hi
Dont be confused by max Ra (rod resistance), 200ohms as suggested in BS 7671 and, max permitted Zs when a circuit is protected by a 30mA RCD = 1667ohms.