We've had a lowest thread how about the highest? obviously scuppered a bit by how high the tester goes but i've had 1147ohms once, terrible ground
 
there is a a product (cant remember the name) its basically crushed volcanic ash which can be used at earth rods to help lower reading. it sucks up all moisture and holds it and so reducing resistance. will did out the name soon.

a) a clay based material formed by the​
decomposition of volcanic ash, such as bentonite
 
Last edited:
Just read on the voltimum site that up to 1660 ohms is acceptable for a TT reading, and it is accepted that over 200 tripping times become unreliable. Will go back to it in a minute but can we discuss this aspect. every one seems to think under 200 is the maximum standard, and me too, have always managed to acheive it so far, thanks to the tips on here.
 
Just read on the voltimum site that up to 1660 ohms is acceptable for a TT reading, and it is accepted that over 200 tripping times become unreliable. Will go back to it in a minute but can we discuss this aspect. every one seems to think under 200 is the maximum standard, and me too, have always managed to acheive it so far, thanks to the tips on here.
On a 30mA rcd its 1667ohms, 200 is the standard as anything above that is classed as unstable ;) niceic like to see less than 100 though
 
Hi

Dont be confused by max Ra (rod resistance), 200ohms as suggested in BS 7671 and, max permitted Zs when a circuit is protected by a 30mA RCD = 1667ohms.
 
Just had mine too, on a C/U change, over 1000ohms. Banged three more rods in and got it down to 800. Back next week armed with 10 more rods, bag of Pompeii's finest and three flasks of coffee!
 
Hi

Dont
be confused by max Ra (rod resistance), 200ohms as suggested in BS 7671 and, max permitted Zs when a circuit is protected by a 30
mA
RCD = 1667ohms.

And 542.2.2 to go with it - "The type and embedded depth of an earth electrode shall be such that soil drying and freezing will not increase its resistance above the required value."
 
Hi

Dont be confused by max Ra (rod resistance), 200ohms as suggested in BS 7671 and, max permitted Zs when a circuit is protected by a 30mA RCD = 1667ohms.


Lenny I do not have that much experience with TT so forgive me, But I know we need a low Ze But isn't it the

Zs that really counts ?

An excerpt from snags and solutions earthing and bonding that I happened to be reading today in the Van.

Talking about an upfront time delayed 100ma rcd (Snag 10) where RA needs to be below 500 ohms

"These values are normally easily obtainable but, unless there are good reasons to expect such high values

such as hard /rocky ground" ---I have to go back to a property next week that has about 565 ohms .

However its concrete on top of slate and slate bedrock Every thing on 30ma Rcds . what would you do in

that situation keep on banging rods till it gets lower and if so how many would you bang in ?
 
Well mate you do need to get it to below 200ohms really.....NIC ask for less than 100 but lets not worry about them for now.

You could try adding more rods, at least the length of the rods apart. Bentonite is cracking stuff, need to make bigger holes in the ground though for it to be of any use.
 

Reply to Highest ze on a tt in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
739
thanks @Julie That is an incredibly detailed answer. I have forgotten a lot of electronics from my college days through lack of use...
2
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top