Evening folks, couldn't change this sparks mind! It was an old boy, I started questioning it but rather than cause a scene I just pacified him and walked away, not my name on the cert! Working in a pub with him and asked what he was testing, turns out it was Zs of lighting circuits by having his socket tester probes plugged into a extension lead on a local socket circuit but the earth lead removed from his meter and instead he had his earth probe lead connected and probed onto the cpc at various points on the lighting circuit to get a Zs. I've never seen that before, doesn't seem right at all!??!! The meter is testing down the socket circuit and back along the cpc of lights, and he said "well, that's what I need to know, just the earth return path" anyone else seen people do this? looks like he was just being lazy and not wanting to remove covers etc!