fog

Hi fitted new 17th edition board in house partial re-wire have 2 rcbo's for the lighting circuits.1 for upstairs and 1 for the downstairs lights
2 downstairs lighting wires one old one new, when the old wire is fitted to rcbo all works ok until the hob, is taking load/power i.e a ring turned on then it makes the rcbo trip on the lighting circuit?
If the lighting circuit wire is fitted to the 6 amp MCB for the smoke alarms there is no problem.
What would be causing the 30ma rcbo to trip, any ideas ? and is it ok to leave this on the smoke MCB?
never had this sort of problem before any ideas welcome thanks
 
Always a pain in the proverbial, my guess would be a shared neutral somewhere in the old install, Would be worth doing some continuity checks between circuits, disconnect from the board first to prevent false readings.
Just a thought . Your new board should be high integrity, if it has two rcd's you should have three neutral bars, with rcbo neutrals on the non protected neutral bar
 
Last edited by a moderator:
Hi BS
you are probably right need to do more checks
Yes it is high integrity board with seperate neutral bars , 3 off
could understand if it was all lighting circuits but cables are 1.0mm for lighting and 6/2.5cpc for the hob circuit.
builder has been in the loft adding extra bracing he may have disturbed something, but more likely to be neutral sharing typical after all is plastered next time will do checks on old circuits before changing board
 

Reply to hob lights trip in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
341
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
681
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top