Hi I have go a bit of home work but im unsure about one of the questions it says

You have been tasked by your supervisor to install a new A3 circuit in the store room for a general workers to use, you go into the distrobution room and see it is a 3phase board with bs 3036 fuses, are you able to comple the task asked by the supervisor, if so explain why?

I think it will be ok to install a A3 circuit on 3036 fuses aslong as the sockets are rcd protected by a rcd either inline or incorporated into the socket.

Would you say that was ok
 
yes, but if cables are buried inn wall/s < 50mm deep. 522.6.101 applies also.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Baker1988

Arms
-
Joined
Location
Kingston Upon Hull
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
homework 3036
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Baker1988,
Last reply from
MDJ,
Replies
4
Views
99

Advert

Back
Top