How do you fault find on a zone valve to see if its working.

What are the dead test that can be done on them to prove the micro sw is working. Also just any test really

Not out time long so i think this is a useful thing to know when working on heating systems
 
Assuming its a 2 port, blue and brown drive it open and will spring shut on de energising.
Therefor you should get a resistance reading at brown and blue, the motor winding.

Grey and orange are the micro switch wires. Put your test leads across them and force the valve open manually, quickly and all the way, and as the internal mechanism gets to fully open you will see a zero ohm reading briefly before the mechanism starts to close.
 
Easiest way to check. Power it up if it doesn't move over the motor is foofed. You don't need to swap the whole valve though you can swap the motor very easily and you can pick them up for about 8 quid. Same motor for 2 port and three port so you can really pick them up from anywhere.
 
Just fault found a three port valve, not working correctly and have told my plumber that it needs replacing, his reply "are you sure it's not the wiring as its a new valve", why don't plumbers like being told when their gear goes wrong
 
reply "are you sure it's not the wiring as its a new valve", why don't plumbers like being told when their gear goes wrong

Because there is no longer apprentices and then electricians whose experience can be judged by their age,appearance of years.

Nowadays you can be looking at a 40 year old , erm, spark who has less than 5 yrs experience.

Somewhere along the way the public, and plumbers, loose confidence in the dilluted trade.

Boydy
 

Reply to honeywell zone valve in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

  • Article
This is an RSS feed of thread: Testing zone valves electrically..? Content of the thread: Can you test zone valves electrically to find out what...
Replies
0
Views
145
  • Question
Thank you for the update. It's always nice to know that a problem has been solved, or at least understood! Unfortunately not all those seeking...
Replies
6
Views
1K
I
  • Article
Baxi system boiler and Opentherm Hello Does anyone know if its possible to connect an Opentherm thermostat such as a Nest to a Baxi 800 System...
Replies
0
Views
164
Ian777
I
The 4 pumps are :- 1. boiler to cylinder 2. C/H and UFH circulating pump 3. UFH dedicated pump after manifold 4. DHW circulating pump. (this just...
Replies
4
Views
2K
  • Question
You need a wi fi switch that is compatible with your switchbot thermostats. Remove the SCR, use the neutral and live to power the wifi switch, and...
Replies
8
Views
716

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks