Hot Neu. / Reverse when on inverter power | on ElectriciansForums
Discuss Hot Neu. / Reverse when on inverter power in the DIY Electrical Advice area at ElectriciansForums.net
Missouri, USA
I have a small camper. When connected to shore power my receptacle tester shows "Correct" (two orange lights). However, when running on my solar generator's (a Jackery Explorer 1000 v2) inverter it shows as "Hot Neu. / Reverse". Is this expected or is there something amiss? If something is amiss then what needs to be done to correct it? (Note: AC appliances seem to be operating without issue when on inverter power.)
Thanks,
Andrew[ElectriciansForums.net] Hot Neu. / Reverse when on inverter power
It may be that when not connected to shore power, there is no ground connection and therefore the tester has no zero volts reference to measure the voltages on either hot or N.
often small inverters like that are designed to run independently to Earth,
an earthing arrangement known as I.T (Isolated "from" Terra)
careful consideration of the manufacturers instructions is required to ensure this is a safe arrangement as sometimes a N-E link should be applied, sometimes a ground rod is required, sometimes the device is only suitable for running a single device and should not be used to power a distribution circuit at all.
Reply to Hot Neu. / Reverse when on inverter power in the DIY Electrical Advice area at ElectriciansForums.net
Thank you. I looked further into transfer switches and that will indeed work for me, and I'll only need one. Perfect. Thanks again.
Thanks again. Looking into it, it seems that the breaker panels in U.S. homes pretty much all employ 15-amp C-curve breakers for the 15-amp...
