Any Ideas! Went to a job the other day on a commercial premises and when I felt the red phase the 25mm tail was red hot. Now when tried a clamp meter red phase was carrying 32 amps blue-32 amps and yellow is 60 amps. Also voltage coming in was 228 volts. Why would red phase get hot when carrying only 32 amps? Would it be anything to do with harmonics?.
 
Any Ideas! Went to a job the other day on a commercial premises and when I felt the red phase the 25mm tail was red hot. Now when tried a clamp meter red phase was carrying 32 amps blue-32 amps and yellow is 60 amps. Also voltage coming in was 228 volts. Why would red phase get hot when carrying only 32 amps? Would it be anything to do with harmonics?.

maybe loose screws clamping cable at connection point
 
It realy depends what its feeding AC,Fridge ect ect work shop thats off when you got there combined with slack connections
even Just a slack connection @32a would cause a right goot heat
 

Reply to hot tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
152
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
962
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
383
  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top