Been to look at a job.
Existing hot tub, been in for over year.
There are no manufacturers instructions, it is sited on concrete, about 25m from fuse board.
The customer is having problems as it is currently fed by what looks to be 1.5mm twin and earth, keeps tripping out when they turn the temp to certain point, also they can smell a fishy smell - the cable melting.
the hot tub came with a 230V industrial plug on it.
from what I can see from the panel inside the tub it requires a 32A supply.
The house is a tns no room on existing cu.
So, I am going to split tails, feed a new 2 way rcd unit, 32A mcb type c, 6mm 3 core swa to 32A rotary isolator.
With regards to earthing, I have read many posts on this but cant decide what is best.
Should I use the house tns earth on its own, or put a rod in also at the rotary isolator, or keep the hot tub separate and just tt the isolator.
I know some instructions ask for a rod, but I cant find them so I am asking what you more experienced guys would do for the best!
Thanks Guys!
Existing hot tub, been in for over year.
There are no manufacturers instructions, it is sited on concrete, about 25m from fuse board.
The customer is having problems as it is currently fed by what looks to be 1.5mm twin and earth, keeps tripping out when they turn the temp to certain point, also they can smell a fishy smell - the cable melting.
the hot tub came with a 230V industrial plug on it.
from what I can see from the panel inside the tub it requires a 32A supply.
The house is a tns no room on existing cu.
So, I am going to split tails, feed a new 2 way rcd unit, 32A mcb type c, 6mm 3 core swa to 32A rotary isolator.
With regards to earthing, I have read many posts on this but cant decide what is best.
Should I use the house tns earth on its own, or put a rod in also at the rotary isolator, or keep the hot tub separate and just tt the isolator.
I know some instructions ask for a rod, but I cant find them so I am asking what you more experienced guys would do for the best!
Thanks Guys!