Further to my last post I finished the hot tub installation today.

In the end I hammered in 2 earth rods but still couldn't get below 200 ohms! So ..............

Re-assessed the install and decided that the hot tub was double insulated, there were no extraneous/exposed conductive parts in the hot tub vicinity and above all the TN-C-S Ze was 0.14 ohms.

Therefore I have gone with suppliers earth ............................ I'm sure this will raise alot of points from those who wouldn't and those who would have done the same!


I did leave the rods in and are connected to the MET at the 1 way dis board for the hot tub. Although useless at 256 ohms!!

Discuss!! lol
 

Reply to Hot Tub Installation (con'd) ! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top