Depending on the requirements of the actual hot tub, the cable size should be adaquate, but it is likely sitting in the attic as a flat grey twin and earth cable.
If you were to extend this to outside, you would need to use something appropriate for outside, as twin and earth can not be used externally.

We still need the electrical requirements of the hot tub to advise fully.
 
Not sure we are getting the full picture here!

The photo of the 2way consumer unit is NOT an RCD but you mention one to the right of it?
I also suspect another CU as a 2way (6 & 16A mcb's) doesn't seem sufficient for storage heaters! or whole house, (ie where are your cooker, ring finals and lighting connected?)

From what the OP said, my understanding is there is a Consumer Unit with fuses that supplies this board so this is where all the house circuits will be. The concern seems to be about not running a new cable front to back of house. If the cable is of the correct size and tests out ok then that should not be a problem. The OP will need a new House Consumer Unit but seems to be aware of that.
Do NOT get confused with the incorrectly labelled Main Switch as others have said it is NOT an RCD and by look of it the shower install was non-compliant as it wasn't RCD protected!

Most likely the shower was a 16th Edition install, if it was it would have been compliant at the time. Probably going to need a new sub board though as Newlec is Newy & Eyre which badged manufacturers products. This being an Electrium (Wylex) MCB which now look obsolete unless you source the secondhand market. This is on the assumption a smaller size MCB will be required.

Can you step back a bit and take a photo of the whole consumer unit(s) set up, including meter if indoors.

This would be helpful just to be 100% on what is actually there.
 
Not sure we are getting the full picture here!

The photo of the 2way consumer unit is NOT an RCD but you mention one to the right of it?
I also suspect another CU as a 2way (6 & 16A mcb's) doesn't seem sufficient for storage heaters! or whole house, (ie where are your cooker, ring finals and lighting connected?)
Do NOT get confused with the incorrectly labelled Main Switch as others have said it is NOT an RCD and by look of it the shower install was non-compliant as it wasn't RCD protected!

Can you step back a bit and take a photo of the whole consumer unit(s) set up, including meter if indoors.
Th box on the right supply’s everything. The box in the middle used to power the storage heaters which have been removed. The box on the left is the old shower mains.

A new consumer unit is being installed the middle box is going. The black box is obviously being upgraded. The cabling for the shower is the easiest way to get power to the back of the house and the hot tub.
 

Attachments

  • IMG_3149.jpeg
    IMG_3149.jpeg
    2.5 MB · Views: 9
From what the OP said, my understanding is there is a Consumer Unit with fuses that supplies this board so this is where all the house circuits will be. The concern seems to be about not running a new cable front to back of house. If the cable is of the correct size and tests out ok then that should not be a problem. The OP will need a new House Consumer Unit but seems to be aware of that.


Most likely the shower was a 16th Edition install, if it was it would have been compliant at the time. Probably going to need a new sub board though as Newlec is Newy & Eyre which badged manufacturers products. This being an Electrium (Wylex) MCB which now look obsolete unless you source the secondhand market. This is on the assumption a smaller size MCB will be required.



This would be helpful just to be 100% on what is actually there.
Have a look at my reply to
From what the OP said, my understanding is there is a Consumer Unit with fuses that supplies this board so this is where all the house circuits will be. The concern seems to be about not running a new cable front to back of house. If the cable is of the correct size and tests out ok then that should not be a problem. The OP will need a new House Consumer Unit but seems to be aware of that.


Most likely the shower was a 16th Edition install, if it was it would have been compliant at the time. Probably going to need a new sub board though as Newlec is Newy & Eyre which badged manufacturers products. This being an Electrium (Wylex) MCB which now look obsolete unless you source the secondhand market. This is on the assumption a smaller size MCB will be required.



This would be helpful just to be 100% on what is actually there.
have a look at my reply to defyG. 👍🏼
 
Depending on the requirements of the actual hot tub, the cable size should be adaquate, but it is likely sitting in the attic as a flat grey twin and earth cable.
If you were to extend this to outside, you would need to use something appropriate for outside, as twin and earth can not be used externally.

We still need the electrical requirements of the hot tub to advise fully.
Can Twin and earth be used outside if it’s in conduit?
 
It's exposure to UV light from the sun that's the problem, so putting it in conduit solves that problem, BUT, if the conduit is exposed to the sun, it will raise the temperature of the cable inside, and reduce its current carrying capacity. This might require an increase in cable size.
Not been mentioned yet, but what are the earthing arrangements of the property?
 
It's exposure to UV light from the sun that's the problem, so putting it in conduit solves that problem, BUT, if the conduit is exposed to the sun, it will raise the temperature of the cable inside, and reduce its current carrying capacity. This might require an increase in cable size.
Not been mentioned yet, but what are the earthing arrangements of the property?
I don’t have a clue, I just posted a picture of the whole board if that shows anything?
 

Reply to the thread, titled "Hot tub supply" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top