W
Welshsparky
Wired a hot tub in 6 months back ... 6mm cable to isolator from db , from isolator to hot tub. the hot tub is only pulling 16 ap but id put a 6mm in asthe customer said they may upgrade in the future.
just had a phone call from the customer to say their is a funny smell from isolator, customer opened isolator and their hasbeen a blow off some sort, RCD did not trip
Any ideas why this would happen?
All connections were as tight as can be and all relevant tests were carried out upon completion
just had a phone call from the customer to say their is a funny smell from isolator, customer opened isolator and their hasbeen a blow off some sort, RCD did not trip
Any ideas why this would happen?
All connections were as tight as can be and all relevant tests were carried out upon completion