House rewire or not to take the job | on ElectriciansForums

Discuss House rewire or not to take the job in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 12, 2021
Messages
5
Reaction score
1
Location
Birmingham
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit.
This is not used only wiring to kitchen box. The customer has no electrical cooker.
The second fuse 30 A feeds connection box. All the socks in the house come to this junction box under floor board in the bath
Room.
The 3rd fuse also I assume goes to same point. The doc conductor is cut off or non existent.I have tested this for r1 and rn and there is no continuity.
Cpc main conductor is 10mm.
Fuse 3 feeds upstairs lights
Fuse 4 feeds down stair lights.
Fuse 5 and 6 Not used.
Should I recommend complete rewire or put new cu divide the sockets circuits 20 A rcbos . The customer can't pay for full rewire.
What should I do. Refuse the job as I don't think it is safe. I have not looked under floor board because he has tiles glued to floor board and then vinyl floor on top.
Your response will be appreciated
Kind regards
Manjit
 
First consideration for rewire is IR readings and visual inspection of the cable, if it is PVC, good IR, and no evidence of rodents, etc, then you can safely reuse it subject to circuits being up to modern specifications.

If the RFC has a break you can't find without unfeasible amounts of effort / redecorating damage then then as you say, either split it to two 20A radials or essentially make it a 20A "spider" that has some of the RFC end-end connectivity but can't be overloaded due to the OCPD selection. Most likely for open RFC is at an accessory that has been DIY changed, but part of your work might be a refresh of all switches/sockets (certainly any with signs of damage, poor readings, or sickly feeling switches) so you get a chance to do that anyway.

Most likely gotcha for the lights with RCD/RCBO protection is borrowed neutral, but some more testing would reveal that.

Less obvious catch is lack of CPC (or not connected up) which might merit a rewire or might force you in to the options in BPG #1 CU change as least-worst solution.

Cooker circuit should ideally be made usable and safe, as likely in the future they might need an electric oven/cooker and it would be there. Again, IR check and end of circuit PFC/PSCC to confirm all is safe should a cooker be attached.

Main earth of 10mm might be an issue as probably should be 16mm, might be easy to fix (if TT earth then adequate).

Others on here have more experience and can offer better advice I'm sure!
 
Sorry about the mistake it is the cpc conductor that is missing. Fuse 2 has 2 2.5 mms twin and earth both sides are connected to the same fuse. The live and neutral are correct. But 1 twin and earth has no cpc conductor. I don't want to put junction box under bath room floor board and the wife are not long to reach the fuse board of the new cu if I change it. The light is 1.5 mm. The cooker wire is 6mm which is not used.
what I think is either put new junction box and separate the sockets with 3 mins 1 for kitchen,1 for upstairs and 3 for down Stair sockets. I don't known what the contactor who wire has done until I can get to this junction box. Only then I can what is done.
Kind regards
Manjit
 
Yes I am qualified electrician. I think I have a problem with my fire kindle which changes text if I don't check.
the customer has 2 2.5 mm twin and earth wires going to fuse 2. 2 red and 2 black. One 2.5mm has cpc going to earth terminal. The 2nd 2.5mm has the cpc conductor cut off. The customer says there is a junction box under the floor board. This is where all the socket wires go into and how they are connected. I don't know until I get to this junction box and see how they are connected. All together there are 8 double sockets. I put my mft tester on low ohms and there no continuity between red wires. Also no continuity between blacks wires.
so it is not a ring circuit. The is only 1 cpc conductor. Where the other is cut off i don't known.
This job was not done by electrician as I see it I have some photos which I will post. My problem is do I take this job of not.
Kind regards
manjit
 
You need to tell the client some investigation is required to verify this circuit. You say the other cpc is cut off is this not at the consumer unit as you say only one is connected.
 
Hello,
The picture of the board and ring main for the socket. looking at the state of things it looks bad. No cpc 2nd wire
[ElectriciansForums.net] House rewire or not to take the job
[ElectriciansForums.net] House rewire or not to take the job
[ElectriciansForums.net] House rewire or not to take the job
 
That’s buried in the wall?

I’m guessing 70’s or 80’s build… so there should be cpcs in every cable, even the lights.

On the cable where there is no cpc, is it just cut off short, or not there at all….

Agree with Westy, looks derelict.

You could, if they don’t want a huge expense, is to rewire in pvc trunking on the surface. Looks crap, but it’s a possibility for a temporary solution.

A full rewire includes a lot more with making good afterwards
 

Reply to House rewire or not to take the job in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

  • Question
Ouch. Danger notice to customer in my book.
    • Like
Replies
1
Views
615
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
811

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top