Hi

I am going to be running a power supply to a small garden shed on a large caravan site, the shed is owned by the owner of the static caravan to which the shed is beside. Closest power supply is the pitch box, I am running a 6mm swa cable from here to shed( in my Mind pretty straightforward run of 8meters or so).
From memory the pitch supply box has 2 4core16mm cables, two 3 p and n loops from other pitch boxes presumably and the armours are bonded together in the pitch box.
The static caravan is a tt system with an earth rod underneath it which I fully understand. My question is how should I earth the small shed? By way Iof separate rod for the shed or can I do a Ze test at pitch box and if a good reading can u earth by way of the earth of the swa's in pitch box? Unsure of earthing arrangement at the supply distribution board as I have not seen it.
Point to further add it is impractical to run supply from the caravan itself as cable run too far and troublesome, thanks
 
Hi

I am going to be running a power supply to a small garden shed on a large caravan site, the shed is owned by the owner of the static caravan to which the shed is beside. Closest power supply is the pitch box, I am running a 6mm swa cable from here to shed( in my Mind pretty straightforward run of 8meters or so).
From memory the pitch supply box has 2 4core16mm cables, two 3 p and n loops from other pitch boxes presumably and the armours are bonded together in the pitch box.
The static caravan is a tt system with an earth rod underneath it which I fully understand. My question is how should I earth the small shed? By way Iof separate rod for the shed or can I do a Ze test at pitch box and if a good reading can u earth by way of the earth of the swa's in pitch box? Unsure of earthing arrangement at the supply distribution board as I have not seen it.
Point to further add it is impractical to run supply from the caravan itself as cable run too far and troublesome, thanks

How will you run the cable ? 708.411.4 does not preclude the use of PME for permanent buildings but a shed isn't is it ?
 
The cable will run under ground. I appreciate pme earthing should not be used on caravan sites,yes it's a shed but would not be regarded as a permanent building.
 
Out of interest is the owner permitted to connect a supply to the pitch box other than that which is agreed ? The box is normally owned by the site, not the van owner, I would have thought limitations to supply would have been provided at the box and the van must use up to those limitations, so you feed the shed from the van ?
 
Fair question but they have had the ok from the site owners and there is a meter in the pitch box which I am planning to take my supply from, obviously the 'consumer ' side. The meter is fed from a 32a mcb all inside the pitch box it all looks good to me. What do you think?
 
Would need to confirm when I go back Steve. It tn-c-s will have to put a rod in and if tn-s I think I can use the existing armours at the pitch box for my earth providing My readings are low enough, would you think that sounds acceptable? Think it's 0.8ohms fit tn-s system
 
Would need to confirm when I go back Steve. It tn-c-s will have to put a rod in and if tn-s I think I can use the existing armours at the pitch box for my earth providing My readings are low enough, would you think that sounds acceptable? Think it's 0.8ohms fit tn-s system

Yea let us know I would refer to 708.521.1.1 in the BGB for bury depths and RCD with a 30mA at source the supply cable irrespective of mechanical protection IMHO
 
Ok thanks for advice it is def rcd protected within pitch box by way of 40 rcd and over current protection from 32a mcb. I just need to ascertain earthing arrangement. If I'm unsure il just go with the earth rod although hopefully its tn-s! Cheers again. Stewart
 
When you test it Stewart let us know the test results mate it will be interesting to see the Ze on a big site like that and be interested to see the Zs in the shed along with the x1 and x5 on the RCD
 

Reply to How best to earth shed on caravan site in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I hate it when a shed is TTd, why can they not be extended from the tn system? popcorn ready
Replies
7
Views
674
  • Question
Hi, How did you get on with the wiring?
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top