Bit confused as to a way around this. Got house extension. im having a 80 amp up grade to incomer but i think it will need 100amp. but they wanna charge nearly ÂŁ2000..
we already took another shower plus some bits of their list but still up there
AM i doing this right.? as i wanted to use this as an assesment..
Old exsisting house circuits
32 ring Up 100% then 40% of other circuits = 32
32 ring dwn 40% = 12.8
6 light
16 Immer 100% f.l = 16
New circuits (customer wanted sep Raidals for app's)
16 Fridge the 40% = 6.4
16 Freezer the 40% = 6.4
16 D/W the 40% = 6.4
16 W/M the 40% = 6.4
16 Boiler the 40% = 6.4
32 Cooker 10amp + 30% f.l = 16.6
40 shower 100% f.l = 40
32 Ring the 40% = 6.4
6 light loads spots
6 light loads spots all 3 circuits 66% max demand = 11.8
Using Diversity from Tab 1b i still 167.6 amps. which is just way over..
am i doing something wrong here. It says i must on notes for Tab 1b that if using this table the max demand for any circuit is the rated current of OP dvice of that circuit..
i cant use tab 1a within it...
pulling my hair abit here .
as i know the house wont ever pull that, BUT how will i explain this to the assesement officer maybe just getting anxious cos its next week... sorry for long one
we already took another shower plus some bits of their list but still up there
AM i doing this right.? as i wanted to use this as an assesment..
Old exsisting house circuits
32 ring Up 100% then 40% of other circuits = 32
32 ring dwn 40% = 12.8
6 light
16 Immer 100% f.l = 16
New circuits (customer wanted sep Raidals for app's)
16 Fridge the 40% = 6.4
16 Freezer the 40% = 6.4
16 D/W the 40% = 6.4
16 W/M the 40% = 6.4
16 Boiler the 40% = 6.4
32 Cooker 10amp + 30% f.l = 16.6
40 shower 100% f.l = 40
32 Ring the 40% = 6.4
6 light loads spots
6 light loads spots all 3 circuits 66% max demand = 11.8
Using Diversity from Tab 1b i still 167.6 amps. which is just way over..
am i doing something wrong here. It says i must on notes for Tab 1b that if using this table the max demand for any circuit is the rated current of OP dvice of that circuit..
i cant use tab 1a within it...
pulling my hair abit here .
as i know the house wont ever pull that, BUT how will i explain this to the assesement officer maybe just getting anxious cos its next week... sorry for long one