C
cardinal
Evening all..
A friend of a friend has had a very lucky escape. Whilst attempting to put up a new fence, he smashed a fence post straight through his main incomer apparently. He says it was no more than 200mm in the ground, and to add insult to a very near serious injury or worse, they have sent him a bill for nearly £900 for the repair!
Anyone know of any reg's or guidelines on minimum depths? I have told him to seek legal advice before doing anything else, but was just interested. Good job it werent a metal shovel or something eh!
Don’t think there is any specific depth in 7671, but most people seem to work on 600mm. The important thing is that it should not be damaged by using a spade etc.
However a old DNO mate told me that they had to work to
LV
Footpaths/Driveways, etc 450mm
Across Roads--------------600mm
Along Roads---------------600mm
Agricultural----------------910mm
</SPAN></SPAN>
Not sure if that’s the case tho.
Who has quoted BS:7671.??? 600mm is the nominal trench depth for cable laying. Normally the cable manufacturers will also quote this depth, when stating current ratings of cables for direct burial....
I've used this depth for so long now, that if it is in the BRB, ....I've never noticed it ...lol!!
Thanks for the replies. I was aware of the 500/600mm but was unsure if DNO's had to adhere to a seperate set of reg's.. Either way its not good. But for them to bill him as well is bizarre. Ill await the results of his legal advice with interest, and just be thankful it didnt result in anything more serious.
What your friend could possibly have as a defence with, is if the DNOs cable wasn't protected by cable tiles or bricks. Especially if the cable wasn't buried deep enough through occupied locations ...ie a domestic garden!!
So what sort of depth was it when your friend hit the cable ....more or less than 600mm???
If the cable was actually at a depth of 200mm and not protected/identified then I'd be arguing the ---- with the DNO.
As Engineer54 has stated, if the area is a domestic garden then it is reasonable to expect the ground to be disturbed by digging etc. and with this in mind, I would argue that the DNO had a duty of care which obviously wasn't exercised!
I'd also be making a bit of noise on the fact that your friend has actually had a near miss as far as health & safety is concerned!
Ian said 'there is no depth in 7671, however we normally go to 600 mil' I was pointing out that anything to do with 7671, whether in the book, any guidance notes or best practice guides, or simply inferred doesn't matter, and we would need to refer to the DNOs regs.
I found something in ESQCR 2002 Regulation 14:
"Cables must be buried at sufficient depth to prevent danger and they must be protected or marked."
DTI Guidance on ESQCR 2002 states that "In consideration of the methods by which cables should be marked or protected, duty holders should make allowance for the environment in which the cables are installed and the risks to those who may need to expose and work on or near the cables in future"
I had to run 4 400mm 3&½ SWA they had to run under 2 railway lines and a road. We had the trench dug at 1500mm depth then laid 4 x 6” welded steel pipes for the cable to go through. At the LV switch gear end we welded 16mm studs to the pipe and connected them with 95mm singles to the main earth. That sub had the best earth path on the site!
I had to run 4 400mm 3&½ SWA they had to run under 2 railway lines and a road. We had the trench dug at 1500mm depth then laid 4 x 6&rdquo; welded steel pipes for the cable to go through. At the LV switch gear end we welded 16mm studs to the pipe and connected them with 95mm singles to the main earth. That sub had the best earth path on the site!
Not a fence post getting through that!lol.
Seriously though that cable should have had a cable identifier over it at that shallow depth.
ian in this posting before rocker
Re: How deep for main incomer?
LV
</SPAN></SPAN>
latest cable depth spec from CN is
cables in footpaths or road-footpaths LV = 450mm 11KV = 600mm 33KV = 750mm
Cables in agricultural land LV = 1000mm 11KV = 1000mm (33KV = 1000mm to top of tile + 75mm below tile to duct)
Cables laid accross roads and along roads LV = 750mm 11KV = 750mm 33KV = 750m
All measurments are to the top of the duct unless otherwise stated.
If it was less than 450mm i would be arguing the point
I did come accross someone who was knocking a fence spike in the very edge of their property boundry and went straight through an 11KV cable. They heard a thump and the lights went out for about 2000 people!! Lucky for them the protection functioned and there were no injuries. They did go very pale when they were told it was ll KV which is funny as it sounds worse than LV. But if you are going to hit one go for the HV as the protection operates a lot faster than a 400A fuse in a sub station. The further you are from the sub the longer the fuse will take to operate and the worse injuries will result.
Moral to this is always use plans and cat cable dig by hand to confirm position etc.
True about that but even the DNO don't know where half there cables run. or more to the point what kind of condition there are in.
In our regulated world yes all new installations are buried so deep and need to be that deep, but we are talking of cables 50, 60 years old.
My brothers neighbour Slough way got a knock on the door a few years back from the local DNO saying they think the streets main cable come through his property, when they got round the back and confirmed it, it was about 3 inches below his damp course and for years he though it was an old imperial waste pipe. It ran the entire length of his house and then into next doors
Maybe he can charge them rent as the farmers do for underground/pylon installations!
Lol that's a point. Not exactly sure how this ended, but I think once the SEEB, which it was then saw this, they changed the route of the cable pretty sharpish.
spot on IQ. i once drilled through a DNO incomer. as it was in a location where it was not expected to be, the DNO accepted responsibility for the repair. buggers would'nt replace my 16mm x 450mm masonry bit though
I've got some builders excavating some foundations at the moment. There are LV cables and gas pipes in the area, so they are having to do much of it by hand. These will be about 50 years old, so it will be interesting to see how deep they are. The founds are 900mm deep, so I'm sure we will uncover them.
All good and correct information. Unfortunately,
thirty odd years in the trade has taught me that the regional electicity companies i.e. Scottish power etc sometimes make it up as they go along. I've seen some shockers over the years (pardon the pun)
Have you an official link for these cable trench depths?? The MV/HV depths are pretty much standard but those for LV are not standard at all. Over 700mm and your into derating territory. The 450mm are just not deep enough to be at a safe depth, unless run in ducts...
As far as i'm aware, all new road crossings are now to be only allowed in ducts, there also supposed to be providing spare ducts for any future requirements. If i remember rightly, the ducts are to be a min of 100mm.
As stated in the post All measurments are to the top of the duct unless otherwise stated. This implies that all cables are to be laid in ducts.
As the cables are laid in ducts derating has to be applied regardless of depth. This is carried out at the design stage, it does not mean that the cables canot be buried at the specified depth.
As far as I know road crossings have always been ducted (there are exceptions) and as you say spares laid for future use.
I have not got a link to post but all figures were taken from the latest spec.
Australia
cardinal,
mechelec,