Hi guys wondering what's the best way to do this got a board change on a TT system 3 bed terrace. So we need to offer an SPD however can't have one in a metal C.U without RCD protection on the Tails because of the single insulation feeding the SPD. So to do that that we need an s type RCD upfront. But we can only use a metal clad enclosure there so the price is rising quite a bit.. Or do I forgo the SPD due to cost and take the Tails directly to the main switch obviously correctly supported and properly glanded this will be for my 1st niceic inspection so want to get it right. Cheers
 
Most likely wont go with upfront rcd due to cost . I would rather not fit the spd to be honest due to the issues it brings up. But if customer wants it I want to make sure its done correctly. Also do I need to worry about the spd type with it being TT. And if so does anyone have a link to a suitible C.U with correct type
 
These are good, but not cheap, and they offer choices for TT and TN options:

But more generally the 1+1 style where you have one SPD element L-N and another from N-E you don't have any single point of failure that would allow a L-N short with all of the danger related to it. There are many cheaper options for that configuration, as it is common in the EU to have TT anyway.
 
Most likely wont go with upfront rcd due to cost . I would rather not fit the spd to be honest due to the issues it brings up. But if customer wants it I want to make sure its done correctly. Also do I need to worry about the spd type with it being TT. And if so does anyone have a link to a suitible C.U with correct type
If you look at the fuseboard prices any additional costs would be minimal. If such costs are making such a dent, with respects you are not charging enough.
 
I think you are over thinking things a little, use a proper tails gland and consider Wilko's suggestion and forget the separate enclosure.
ok that probably is the case as this will be my 1st inspection just need to make sure on the correct spd type never really thought about it before they have just gone straight in on tn systems.
 
In addition, rcd's / rcbo's have a tendency to fail when you don't want them to. As with TT they will not be additional protection I would definitely go with an upfront time delayed DP RCD. I do not believe you have to, but that would be my preference.
ahh ok in replacement of the main switch wouldnt this mess with any spd tho as it would be down stream. but yes good shout
 
I've got to be honest, I'm not so sure about an SPD with TT unless you have a pretty good Ra - I will leave that for others to comment for now as off to bed :)
Most electronics is at risk from the L-N volts, so the (typical) MOV SPD covers that. The N-E will normally have a higher damage voltage, so the GTD is enough protection before cables flash over or class-Y filter capacitors go pop.

If you are TT on the end of a long rural cable you might want to look at the type 1+2 SPD that can divert a lot more energy, much as you would if the building has lightning protection. Usually though in the UK the flash density if fairly low.
 
Most likely wont go with upfront rcd due to cost . I would rather not fit the spd to be honest due to the issues it brings up. But if customer wants it I want to make sure its done correctly. Also do I need to worry about the spd type with it being TT. And if so does anyone have a link to a suitible C.U with correct type

A Fusebox time delay RCD is only about ÂŁ40. If you are trying to contain the cost for the customer, just fit this out of your own pocket and regard it as "insurance" against NICEIC raising a problem not having one installed during your assessment. Also, the Fusebox SPD now sits after a 32A MCB (originally there was no MCB, but they changed that last year).
 

Reply to How do I comply TT system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
587
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top