TT system wired about 10 years ago, using a 16th Edition board but with no 100mA RCD as main switch. (muppet!)

As it stands the 30mA doesn't trip and so needs changing anyway.

Whats the best way to protect the non RCD circuits without spending a fortune? The options I think I have are:

1) Change main 100A switch for a 100mA time delayed RCD - as it should have been in the 1st place

2) Change main 100A switch with a 30mA RCD - trouble is there is no discrimination with the other RCD in the board! Or don't even bother changing the other RCD and just have 1 protecting all circuits!

3) Change non RCD MCBs with RCBOs - too expensive.

Anyone got another option? I'm inclined to do No. 2.
 
When I used a TT for my assessment there was no 100mA RCD as a main switch, there was a dual RCD CU with 30mA protection to every circuit.. This was perfectly acceptable
If all circuits had 30ma protection then there would be no need for a 100ma, depending on the amount of non protected circuits then board swap as tel says sounds the better option
 
Legrand board.

I reckon changing MCBs to RCBOs would be cheaper than changing board but customer doesn't want to pay that sort of money. Its been like this for 9-10 years and obviously customer asks why do I need to spend money on this? I'm twisting her arm to do something at least.

Sorry I thought the question was directed at me.
 
If this is your typical 200 ohm UK TT system, then it's got to be all RCBO, with a 100mA RCD front end!! .... As wirepuller says it'll not be too often, you'll get two RCD devices failing on you at the same time... lol!!
 
If this is your typical 200 ohm UK TT system, then it's got to be all RCBO, with a 100mA RCD front end!! .... As wirepuller says it'll not be too often, you'll get two RCD devices failing on you at the same time... lol!!

Ze isn't that bad 13 ohms ish. Ideal situation would be to put RCD and RCBOs but in the real world some people can't afford it!
 
I had 1 similar to this recently although it was a tncs system.

The problem I had was that I had carried out alterations to a few of the circuits on the main switch side of a 16th ed split load board meaning I had to rcd protect them as the cables were buried in the plaster.

It was a tight board so rcbos simply would not fit. The way I saw it I had 2 options.

1. move mcbs across to rcd side and buy new busbar comb as the existing did not have enough spares

2. Replace main switch with 30mA rcd and as the links were flexible, feed the 2nd rcd from the supply side of the main one so they are not connected in series.
I was fortunate in this case as there was an isolator switch in the meter cabinet so I removed the "Main Switch - isolates all circuits " sticker and made a warning label stating "isolate at meter cabinet"

This may be an option for you to consider.
 
2. Replace main switch with 30mA rcd and as the links were flexible, feed the 2nd rcd from the supply side of the main one so they are not connected in series.
I was fortunate in this case as there was an isolator switch in the meter cabinet so I removed the "Main Switch - isolates all circuits " sticker and made a warning label stating "isolate at meter cabinet"

This may be an option for you to consider.

Yes I've seen that before but forgot all about it - thanks.
 

Reply to How do I make this safer than it is now? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
626
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K
  • Question
It is six of one and half dozen of the other. PME to the supply RCD is easy and allows OCPD disconnection so simpler DB to feed it all. But then...
Replies
6
Views
1K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
831

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks