TT system wired about 10 years ago, using a 16th Edition board but with no 100mA RCD as main switch. (muppet!)
As it stands the 30mA doesn't trip and so needs changing anyway.
Whats the best way to protect the non RCD circuits without spending a fortune? The options I think I have are:
1) Change main 100A switch for a 100mA time delayed RCD - as it should have been in the 1st place
2) Change main 100A switch with a 30mA RCD - trouble is there is no discrimination with the other RCD in the board! Or don't even bother changing the other RCD and just have 1 protecting all circuits!
3) Change non RCD MCBs with RCBOs - too expensive.
Anyone got another option? I'm inclined to do No. 2.