Hi, I am not an electrician but desperatly need to know the basic guide on how to test an earth stake and what test equipment is required? I'd appreciate any response to be really basic, enough for a me to understand! Many thanks in advance.
 
There are two different Methods for testing TT which I'll explain later when I'm sat at home. But please consider that testing is not easy and should be taken seriously therefore I suggest asking an electrician to do it. Because regarding which method of testing you choose a different tester is required.
 
Hi, I am simply trying to understand it bit will not be carring out myself! Trying to gain some knowledge so as not to have rings run around me.
 
Usual method is to use a Loop Tester which is connected to the phase and neutral at the consumer unit and the green/yellow cable connected to the stake. The reading is in ohms and should be below 200, the lower the better.

Alternatively you can use an earth electrode tester which is a long winded way of doing it, most sparks will use the loop tester.
 
the easiest method is the EFLI method. it is exactly the same as taking a Ze measurement, using the earth rod, instaed of a suppliers earth. this method is only to be used on domestic TT systems.

For large premeises, the easiest method is the fall of potential method. Lenny posted a guide a while ago. ill try and find it
 
http://www.------.org/publishing/wiring-regulations/mag/2006/21-ttsystem.cfm?type=pdf

The above link was designed for the 16th edition but is a very good explanation of a TT and therefore how to test and Earth electrode.
 
Hi, thank you.

Would anyone have the patience to write a step by step guide please?

Everything you might want to know is in Guidance Note 8, Earthing and Bonding particularly for RA method, else measure Ze. You shouldn't undertake either test though, unless you know what you are doing
 
just out of interest, why can't you use the Loop tester to test the electrode on an installation other than a domestic?

There is no specified building type for the loop tester method, the only stipulation is that the installation is protected by an RCD.
 
How so, and surely it's what BS7671 says that matters no the OSG?

When you're measuring Ra values of around 100 Ohms as you are for most RCD protected TT systems then accuracy isn't quite so critical so the EFLI method is perfectly adequate.

If however, you're measuring Ra or Rb values for say a generator or transformer then accuracy is far more important so an earth electrode resistance tester is the instrument of choice (This is a common 2391-10 question).
 
Usual method is to use a Loop Tester which is connected to the phase and neutral at the consumer unit and the green/yellow cable connected to the stake. The reading is in ohms and should be below 200, the lower the better.

Alternatively you can use an earth electrode tester which is a long winded way of doing it, most sparks will use the loop tester.

Has anyone used a Metrel/Alphatek1557 mft for this?

If so, what setting do you use?
 
When you're measuring Ra values of around 100 Ohms as you are for most RCD protected TT systems then accuracy isn't quite so critical so the EFLI method is perfectly adequate.

If however, you're measuring Ra or Rb values for say a generator or transformer then accuracy is far more important so an earth electrode resistance tester is the instrument of choice (This is a common 2391-10 question).


And..... Don't forget Lightning Protection systems, need to use an earth electrode resistance tester here too!!!
 
Has anyone used a Metrel/Alphatek1557 mft for this?

If so, what setting do you use?


Like other MF Testers when used for earth rod testing using aux test electrodes, .... It's fine for domestic and light to medium commercial installations!!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
How do I test an earth stake - please help!
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
matt25,
Last reply from
Engineer54,
Replies
17
Views
22,172

Advert

Back
Top