Assuming that you measure the windings for a power transformer, for example:
A-B: 2,258 ohms
B-C: 2,262 ohms
A-C: 2,250 ohms, how do you calculate the tolerances for these? What formula do you use? You consider as reference the highest or the lowest value from every 2 readings?
I just wanna check an industry tollerance of +/- 5%.
Thanks.
 
Are these dc resistance measurements?

Assuming for now they are then:

1. Find the mean average of the resistances of the three windings. Thus Rmean = (2258 + 2262 + 2250) / 3;

2. Find the percentage difference D of each winding resistance from Rmean. Thus for example for the first winding

D1 = (2258 - Rmean) x 100 / Rmean

3. Now compare D1, D2 and D3 to +/- 5%
 

Reply to How do you calculate the tollerances from a 3 phase winding measurement in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
798
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top