Well that reminds me, if you were doing an insulation resistance test on a row of LED lights, would you have to disconnect them all if they had sensitive electronic parts in themAlso if you are testing L+N to E (as you would do for any vulnerable electronics like non-removable LED lights) then you won't see the neon.
During installation you really should try and test L-N before the lights go in, afterwards you probably would just test L+N to E (connected to MET) as disconnecting and reconnecting adds the risk of introducing more faults than you might have started with.Well that reminds me, if you were doing an insulation resistance test on a row of LED lights, would you have to disconnect them all if they had sensitive electronic parts in them
Right interesting, cheers.During installation you really should try and test L-N before the lights go in, afterwards you probably would just test L+N to E (connected to MET) as disconnecting and reconnecting adds the risk of introducing more faults than you might have started with.
If it is wired in T&E (most domestic, quite a lot of the rest) then the CPC lies between L & N anyway so most cable damage or faults will show up as L or N to CPC fault within the cable, or L/N to external fault back via MET if cable cut/crushed against steelworks, other cables, etc.
Not if you are fault finding, had a job RCD/MCB tripping out on 32A RFC , when spilt down circuit and testing located the damaged cable between two sockets 0meg ohms across LNE, I always check both ends same results.In the real World you will rarely do an IR test L to N except for a brand new circuit. Usually L&N To E is all that’s needed.
L to N IR tests on existing installation is fraught with hidden issues : TV Amp in lofts, smart switches and (worst) sockets with built in USB sockets. ?
In the real World you will rarely do an IR test L to N except for a brand new circuit. Usually L&N To E is all that’s needed.
L to N IR tests on existing installation is fraught with hidden issues : TV Amp in lofts, smart switches and (worst) sockets with built in USB sockets. ?
Is that a serious question, mate?When you know there are accessories connected which you can't find which give a 0.00 IR reading when testing L to earth and N to earth seperately, would testing L+N together to earth give a reading in that instance?
Yes, would have been a bit pointless and random if it wasn't!Is that a serious question, mate?