C

Capn Ahab

CU in hallway, water pipes into house are out the front door and round the other side of the house. Probably a 6 -7m main bonding conductor.

a) Is this safe?

b) Is there a way of testing it without using really long leads?

Cheers,

Ahab
 
CU in hallway, water pipes into house are out the front door and round the other side of the house. Probably a 6 -7m main bonding conductor.

a) Is this safe?

b) Is there a way of testing it without using really long leads?

Cheers,

Ahab

You answered your own question, you use an R2 long lead test to ascertain the resistance of the bonding conductor.

This should be within approximately 0.05 Ohms

Your 'is it safe' question is quite surprising, what experience do you have?
 
Yes basically "method 2 - R2" we had to do this in an old peoples home when it was empty, just make sure you null the whole lead.
 
Unless you can physically trace the cable, then you should really isolate the supply to the installation in question and disconnect the cable at both ends and then carry out the continuity test.

This is only my opinion, so please don't take it literally as being correct.
 
Unless you can physically trace the cable, then you should really isolate the supply to the installation in question and disconnect the cable at both ends and then carry out the continuity test.

This is only my opinion, so please don't take it literally as being correct.

Just for 2391-10 students, the installation should always be isolated when testing main protective bonding conductors.
The method in Guidance Note 3 recommends the disconnection of one end of the conductor to avoid parallel paths.
 
Your 'is it safe' question is quite surprising, what experience do you have?[/QUOTE]

Thanks for the answer. I suppose it was a bit of a dumb question with hindsight as a little thought process would tell me that as long as the ohms are low enough it is safe. What I meant was, since I don't know anything other than the 17th ed, is there anything that was allowed in previous editions of the regs that wouldn't be now, e.g. Is running the main bonding conductor along the outside of the house acceptable? I'm just starting out to be honest and want to get things right, but don't know the BRB back to front yet.

Thanks to all for the surprisingly quick answers BTW.
 
Just for 2391-10 students, the installation should always be isolated when testing main protective bonding conductors.
The method in Guidance Note 3 recommends the disconnection of one end of the conductor to avoid parallel paths.

I disconnect it at both ends to identify as well as the continuity test so I can cable tie a tag displaying the words Gas or Water or Steelwork and that's in all honesty and that was a requirement of the nic for a new install so I used to carry it out on remedials while carrying out pirs.
 
Your 'is it safe' question is quite surprising, what experience do you have?

Thanks for the answer. I suppose it was a bit of a dumb question with hindsight as a little thought process would tell me that as long as the ohms are low enough it is safe. What I meant was, since I don't know anything other than the 17th ed, is there anything that was allowed in previous editions of the regs that wouldn't be now, e.g. Is running the main bonding conductor along the outside of the house acceptable? I'm just starting out to be honest and want to get things right, but don't know the BRB back to front yet.

Thanks to all for the surprisingly quick answers BTW.[/QUOTE]

It's unusual, the bond is normally carried out at the point of entry to the building.
 
as long as the cable is not prone to be damaged, no problem. any chance of mechanical damage, it should be protected in conduit. are there hungry squirrels about the property?
 
The outside cable can be made squirrel proof by

A, Enclosing the cable in conduit or
B, Make sure the squirrel has an abundance of nuts or
C, Buy a cat
 

Reply to How do you test main bonding when it's several meters long? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top