hello my colleagues electricians
I need to wire 7,5 kW cooker, the cable run will be 15 meters clipped direct what would be the MCB and cable size. from my calculation I work out it should be 40A B MCB and 6mm2 twin&earth but can anyone tell me if I can use 4mm2 instead and/or 32A B MCB.
Ib=P/V=7500/230=32,6 but who has ever used the full power of an appliance?
I also checked the voltage drop and Zs for both cable sizes and MCBs just need to make sure that 40A and 6mm2 T&E won’t be overestimated.
any advices?
regards
Michael
I need to wire 7,5 kW cooker, the cable run will be 15 meters clipped direct what would be the MCB and cable size. from my calculation I work out it should be 40A B MCB and 6mm2 twin&earth but can anyone tell me if I can use 4mm2 instead and/or 32A B MCB.
Ib=P/V=7500/230=32,6 but who has ever used the full power of an appliance?
I also checked the voltage drop and Zs for both cable sizes and MCBs just need to make sure that 40A and 6mm2 T&E won’t be overestimated.
any advices?
regards
Michael