''I had an interesting fault the other week whilst checking that Class 1 metal socket fronts were earthed. Admittedly it would have been best to carry out whilst dead, however this was just a quick check for peace of mind after doing a different job at night. I found 50v between the metallic light switch front and the main earth terminal at the consumer unit. When the light switch was switched on there was 100v. Further examination showed that the CPC (Earth) to the light switch was disconnected in the ceiling rose. Tests of the earth at the rose proved ok, IR tests on the switch cable proved ok. Reconnection of the CPC (earth) eliminated the problem. All I can put this down to is induction from the live conductors to the CPC conductor. One to look out for though''

originally posted by
topcop999

can anyone please explain why this happens?
Is it down to induction ?

thanks chris
 
Had a lady tell me that she kept getting electric shocks off her light switches. Her husband had told her it was just static.
I tested from main earth terminal to faceplate screws and read 230v
When the fuse board cover was opened up you could see that the shower cable had melted against the lighting circuit
 
Was the lighting cpc not connected at the board then? Should have been a big bang, not shocks from switch plates!

Or had that happened and blown the lighting cpc to smithereens and the shower fuse replaced?

Simon.
 
eons n eons ago as an apprentice i was screwing a switch plate back using a paint tin opener and it glowed we found the fauld was gompressed cable Joist had been cut to accomodate cables but cut wider than board leaving floorboards resting on cables and broken earth 6mm twe next to the 1.m we traced was squished so much it was same depth as 1.5mm but 4times as wide opened sheath and found the copper strands al spread out
 

Reply to how does a broken earth have volatge on it??? in the Talk Electrician area at ElectriciansForums.net

Similar Threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
Hello What was the conclusion of your problem?
Replies
1
Views
721
  • Question
No and why are they not earthed??? Presumably there's no CPC in the cable?
    • Like
Replies
10
Views
2K
As above. Also PME doesn't exist outside the UK. Almost all installations within the State are TN-C-S - TT has pretty much been eradicated...
Replies
2
Views
3K
  • Question
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
    • Like
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks