Hi gents,

It's straight forward that in an event of a fault earthing will deliver current from exposed metal parts(electrical accessories) to the Earth, and it grounds to Earth potential.

So the question is, if for example, in lighting circuit a fault occurs, how it will go from a ceiling rose(which is plastic) to the earth if the earth wire is not connected directly to the lamp? Does it mean that the ceiling rose will become an exposed part and then earth will be in the game?

[ElectriciansForums.net] How earthing actually works in a fault
 
Hi gents,

It's straight forward that in an event of a fault earthing will deliver current from exposed metal parts(electrical accessories) to the Earth, and it grounds to Earth potential.

So the question is, if for example, in lighting circuit a fault occurs, how it will go from a ceiling rose(which is plastic) to the earth if the earth wire is not connected directly to the lamp? Does it mean that the ceiling rose will become an exposed part and then earth will be in the game?

View attachment 29048

The most important part of your question I've highlighted.

Have a little think.
 
you can't have an earth fault on a 2 wire lamp. only a L-N fault will trip the OCPD.
 
The most important part of your question I've highlighted.

Have a little think.

Plastic is a good insulator. I can't really see how the ceiling rose can become exposed.. only if it still conducts some electrical charge.

you can't have an earth fault on a 2 wire lamp. only a L-N fault will trip the OCPD.

Why then earthing is necessary for the circuit ? Because of potential difference?
 
Last edited:
earthing is required up to the end of the circuit cable to protect against earth faults in the cable itsef. it's only connected to fittings if they have conductive parts. otherwise the cpc is just terminated in a blank connector or connected to a terminal provided for it. e.g. as you find in a plastic patress.
 
earthing is required up to the end of the circuit cable to protect against earth faults in the cable itsef.

Could you please elaborate this? Can't really grasp the meaning..

otherwise the cpc is just terminated in a blank connector or connected to a terminal provided for it. e.g. as you find in a plastic patress.

So the cpc is not necessary there?
 
Last edited:
to put it over simply, if someone bangs a nail into the cable, shorting out the L and cpc. the OCPD will interrupt the supply
 
Could you please elaborate this? Can't really grasp the meaning..

If the cable deteriorates and causes a short or (more likely) accidental/careless misuse by others (screwing/nailing things in the wall).


So the cpc is not necessary there?
Regulation 411.3.1.1 tells you that "A CPC shall be run to and terminated at each point in wiring and at each accessory except a lampholder having no exposed-conductive-parts and suspended from such a point."

So the "such a point" is the ceiling rose, and the "lampholder having no exposed-conductive-parts" is the bit of plastic you attach your lamp to, suspended by the white bit of two core flex.

The reason for this regulation is that, even if all your accessories have no exposed-conductive-parts, they could at any time in the future be replaced for metal ones. Wiring systems are installed to last a long time.

Hope that's helpful :)
 
to put it over simply, if someone bangs a nail into the cable, shorting out the L and cpc. the OCPD will interrupt the supply

But the OCPD will interrupt the supply even without the cpc, isn't it? And if someone will bang the nail just in the cpc, nothing will happen to the circuit and the OCPD will not be fired, right?

If the cable deteriorates and causes a short or (more likely) accidental/careless misuse by others (screwing/nailing things in the wall).



Regulation 411.3.1.1 tells you that "A CPC shall be run to and terminated at each point in wiring and at each accessory except a lampholder having no exposed-conductive-parts and suspended from such a point."

So the "such a point" is the ceiling rose, and the "lampholder having no exposed-conductive-parts" is the bit of plastic you attach your lamp to, suspended by the white bit of two core flex.

The reason for this regulation is that, even if all your accessories have no exposed-conductive-parts, they could at any time in the future be replaced for metal ones. Wiring systems are installed to last a long time.

Hope that's helpful :)

Thanks that was really helpful! Much appreciated. :)


But I can't really see why the cpc is protecting "against earth faults in the cable itsef". Even if the cpc will be faulty in the circuit, it shouldn't matter because it's not used at all?
 
Last edited:
But I can't really see why the cpc is protecting "against earth faults in the cable itsef". Even if the cpc will be faulty in the circuit, it shouldn't matter because it's not used at all?



​you will get the fault if the L is shorted to the cpc. this is because the cpc is connected to the MET @ 0V and so a short will give rise to a fault current of sufficient magnitude to trip the OCPD. ( we hope).
 
But I can't really see why the cpc is protecting "against earth faults in the cable itsef". Even if the cpc will be faulty in the circuit, it shouldn't matter because it's not used at all?



​you will get the fault if the L is shorted to the cpc. this is because the cpc is connected to the MET @ 0V and so a short will give rise to a fault current of sufficient magnitude to trip the OCPD. ( we hope).

I understand that if L is shorted to the cpc then more current will be dragged because of the additional cpc length, therefore =more current used =there's a fault = OCPD in use. Am I right ?

The question is, if only the cpc will be nailed in that circuit, it won't compromise the circuit. Therefore the cpc doesn't have any practical usage over there, isn't it? It more has "decorative" function, just because it's stated in Regulations that : "A CPC shall be run to and terminated at each point in wiring and at each accessory except a lampholder having no exposed-conductive-parts and suspended from such a point." only because of that we need the cpc there.

Thanks!
 
Last edited:
i advise some serious reading, as you don't seem to have a grasp of the fundementals.
 
several you tube videos by chris kitcher are worth watching. also google earthing and bonding. see what you find
 

Reply to How earthing actually works in a fault in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi I need help with understand supplementary bonding. I know RCD is additional protection and in the even of the fault at leakage of 30mA, it...
Replies
0
Views
37
  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
618

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top