I have a customer whose socket has a cracked front plate on it. The house wiring is still original and as such has a wylex fusebox and undersized bonding conductors. I have replaced the front with a new one and tested that circuit as I saw it as an immediate danger and have then told the customer tat she needs to have the house wiring inspected and that it would lead to a new consumer unit and main bonding having to be installed.

Did i go too far? Thing is when it comes to domestic work i don't want to mess around. There are too many stories of fines and imprisonment over such things. Much prefer industrial work.

Thanks in advance!
 
I carried out an r1+r2 fig 8 test, IR, polarity, PSCC & Zs test on the socket circuit and at the supply i carried out a Ze, PSCC and polarity test. All of which were satisfactory. The point being that realistically should i have corrected the bonding conductors and installed an rcd on the circuit before replacing the socket front?
 
There is a balance to this as the customer wants the socket fixed and you are doing your job by highlighting that her system has come to the end of it life.

The only problem is she may think you are trying the hard sell on her ie the old adage of going into a well know lets just say a "Tyre replacement company" with a puncture and you come out with 4 new tyres new shocks and a battery its not until you get home and feel "was I ripped off"

So best thing to do is if the customer wants a replacement socket plate then you can either do the job and highlight the rest or give the installation a quick check then inform the customer either way its their decission.

If you push it they may feel under pressure and get someone else. I was asked to quote for a new CU for an old biddy the only problem was that the VIR cables in the fuseboard were crumbling so I pointed out that the house neeeded a complete rewire and highlighted that I did not quote for rewires and that just changing the CU would just cause more problems. I was thanked for my honesty from her and her daughter so yep I lost a job but built a reutation.
 
IMO replace socket front and advise a PIR as you have visualy observed things which concern you remember that the installation was done before the 17th and probably the 16th and Could not "Would" need a new CU put your recomendation to PIR in writing with a quote for doing PIR
 

Reply to How far should i go? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
60
  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
389
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
347

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
Thank you, much appreciated Dan
    • Like
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top