There are no specific regs as to how long it is.
However it will have to meet regulations regarding volt drop calculations.
 
as long as the Zs at the spurred socket is below 1.09 ohms it's good (assuming a 32A type B MCB), and of course VD below 5%. (11.5V).
 
If if longer than a drum of 2.5 then its too far...:cool:
In all seriousness if we are talking domesticated dwellings then it’s unlikely to ever exceed maximum permissible lengthy
 
I want t run a spur(using 2.5mm cable) from a socket on a ring main . how long can the spur cable be?
Lots of imponderables to deal with Voltage at final destination ( have any volt drop calculations been done?)
[automerge]1570541797[/automerge]
not sure how to do v/drop calc , the spur will be approx 4m. i want to run a tumble dryer from the spurred socket
What is the Electrical load of the tumble dryer?
 
if you're going to run 4m 2.5 cable, why not run 2 cables and extend ring in existing socket using wagos or ideal in line splice connectors. it's less than a fiver for extra materials
 
Lots of imponderables to deal with Voltage at final destination ( have any volt drop calculations been done?)
[automerge]1570541797[/automerge]

What is the Electrical load of the tumble dryer?
[/QU
if you're going to run 4m 2.5 cable, why not run 2 cables and extend ring in existing socket using wagos or ideal in line splice connectors. it's less than a fiver for extra materials
thought about extending ring but nearest point to break into it easily and fit conector block will be 6/7m . The 4m length would be fed from back of socket.
 
why can't you run 2 legs from the socket. joint in back box?like here?

rfcextend.jpg
 
thought about extending ring but nearest point to break into it easily and fit conector block will be 6/7m . The 4m length would be fed from back of socket.
You will need to be certain that the socket you intend spurring from is actually part of a RFC and not already a spur from the RFC, and your addition is NOT a spur from an existing Spur
 
You will need to be certain that the socket you intend spurring from is actually part of a RFC and not already a spur from the RFC, and your addition is NOT a spur from an existing Spur
the socket I am intending to spur from is part of the ring main. and is not a spur
[automerge]1570543634[/automerge]
if you're going to run 4m 2.5 cable, why not run 2 cables and extend ring in existing socket using wagos or ideal in line splice connectors. it's less than a fiver for extra materials
thanks , will have another look at options
 
the socket I am intending to spur from is part of the ring main. and is not a spur
[automerge]1570543634[/automerge]

thanks , will have another look at options
see picture in post #9. it's 1 I did last year. obviouslytrhe red/blacks are existing. the brown/blues are my rfc extension., clipped about 3m under floor in crawl space. ( this is what thin apprentices are for. :):):)).
 
because today he wants to run a tumble dryer; next week he may want a dishwasher and a washing machine in the same location. as it's only a 4m run, why skimp for the sake of a few quid?
nope
because today he wants to run a tumble dryer; next week he may want a dishwasher and a washing machine in the same location. as it's only a 4m run, why skimp for the sake of a few quid?
but at the moment he wants to run a tumble dryer, end of, perhaps he might want a sauna, who knows, but for a tumble dryer, its fine
 
nope

but at the moment he wants to run a tumble dryer, end of, perhaps he might want a sauna, who knows, but for a tumble dryer, its fine
don't dispute that, but for the cost involved in extending the rfc, why limit the work to a single accessory point.
 
Its a tumble dryer, unless I've missed something it won't be 4.5Kw, even if it was, its still not 20 amps, why do you think spurs are legal Telectrix, you're over complicating it, no need to extend the ring
 
so you'd be happy pulling 4.5 kW off a double socket, rated at 20A?
There is no reason why not, two laundry appliances are often plugged into a double socket and neither appliance will pull full load constantly even when running together. 4.5kw equates to 19.6a @ 230v, in practice it's likely to be 18.75a @ 240v. I would not claim a spur would be the best way to do it, but neither is it wrong, especially as the OP has stated the intention is only to run one appliance.
 
Its a tumble dryer, unless I've missed something it won't be 4.5Kw, even if it was, its still not 20 amps, why do you think spurs are legal Telectrix, you're over complicating it, no need to extend the ring
mupost was in reply to fairlight's post re tumble dryer and washing machine both on a twin outlet. each will have a 2.2kW heater. add a bit for the restof the machines'bits.... 4.5kW.
i don't disputethatfor 1 appliance aspur complies, but that the cost and effort to extend ring is minimal.
[automerge]1570605483[/automerge]
this had a washer and tumble dryer connected.
1570605480678.png
 
Last edited:
i don't disputethatfor 1 appliance aspur complies, but that the cost and effort to extend ring is minimal.
It complies for two appliances plugged into a double socket on a spur. A preference for a ring is a perfectly legitimate point of view. But to suggest that a spur supplying a twin socket does not comply is plain wrong. And regardless of a ring or spur, the load on the socket will be the same.
 
I'm not arguing that it complies or not. just that for what's involved, extending the rfc would be my preference. with a spur, if OP were to want another outlet adding at some time, he'd have to retro fit a FCU.
 
The pic you have posted above of the burnt out socket shows both line pins overheated, this is probably due to a poor quality socket or plug top, and with those two appliances plugged into that twin socket it would make not a scrap of difference whether it was on a ring or a spur.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
london
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
how long can a spur cable be
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29
Unsolved
--

Advert

Thread statistics

Created
oldandtired,
Last reply from
Zerax,
Replies
29
Views
10,712

Advert

Back
Top