I am currently training as an electrician and have been set a question and was hoping someone please explain to me how to calculate the connected load if I have a mixture of single phase and three phase loads, and I have a three phase service connection from the utility.
For instance, is the following correct:
1. Single phase load (between line-neutral) 100% on each phase, trying to distribute as uniformly as possible between the 3 phases.
2. 3-phase load (irrespective if delta or Y) 33.33% of each on each phase.
3. (1-phase load (2-pole-load) line-line): 50% of each on the 2 phases involved.
3. Add up loads for each phase
Example:
5 Loads (Line-Neutral) (kVA): 1,5,4,2
3 Loads (3-phase)(kVA): 3,6,2
2 Loads (Line-Line) (kVA): 3,4
An example of load distribution between phases would be:
Phase A: 1 + 2 + 3/3 + 6/3 + 2/3 + 4/2 = 8.66 kVA
Phase B: 5 + 3/3 + 6/3 + 2/3 + 3/2 = 10.16 kVA
Phase C: 4 + 3/3 + 6/3 + 2/3 + 3/2 + 4/2= 11.16 kVA
The total connected load (for the entire 3-phase system) is 29.98 kVA. The connected load for each phase is as indicated above.
Dividing the total load by 3 (number of phases) (29.98/3 = 9.99) you get the average load.
1) If someone asks me what are the supply requirements that they would have to provide for the system, would it be 3 phase 400v + E at 29.98 KVA or 9.99KVA??
2) What size would the protective device for the main incoming supply be??
Thanks in advance
For instance, is the following correct:
1. Single phase load (between line-neutral) 100% on each phase, trying to distribute as uniformly as possible between the 3 phases.
2. 3-phase load (irrespective if delta or Y) 33.33% of each on each phase.
3. (1-phase load (2-pole-load) line-line): 50% of each on the 2 phases involved.
3. Add up loads for each phase
Example:
5 Loads (Line-Neutral) (kVA): 1,5,4,2
3 Loads (3-phase)(kVA): 3,6,2
2 Loads (Line-Line) (kVA): 3,4
An example of load distribution between phases would be:
Phase A: 1 + 2 + 3/3 + 6/3 + 2/3 + 4/2 = 8.66 kVA
Phase B: 5 + 3/3 + 6/3 + 2/3 + 3/2 = 10.16 kVA
Phase C: 4 + 3/3 + 6/3 + 2/3 + 3/2 + 4/2= 11.16 kVA
The total connected load (for the entire 3-phase system) is 29.98 kVA. The connected load for each phase is as indicated above.
Dividing the total load by 3 (number of phases) (29.98/3 = 9.99) you get the average load.
1) If someone asks me what are the supply requirements that they would have to provide for the system, would it be 3 phase 400v + E at 29.98 KVA or 9.99KVA??
2) What size would the protective device for the main incoming supply be??
Thanks in advance