I have been tasked with seeing if a site is capable of accommodating a large new installation.
I have done some working out but I'm not sure if I am going down the right lines, as this is not my area of expertise.
The site has a main fused switch disconnector on the main incoming supply, rated at 315amp. This then feeds a 300amp isolator, which provides power to the busbar chamber, where all the various DB's are fed from.
I have received usage data from the energy supplier. They have provided data from the previous 9 months. I have chosen the month with the highest usage. This was 13347.7kwh. This was over a 30 day period. I have then taken this value and divided it by the usage time over that 30 day period.
The site was running for 22 days out of 30, and for 10 hours a day. This gives me 220 hours running time. Therefore, I should have a kw value of 60.67kw (13346.7/220).
I have then used the 3 phase power formula, P=root3 x VL x I x Cos(theta), to find I. I have used a line voltage of 440 and an estimated power factor of 0.9.
I = 60.67kw/root3 x 440 x 0.9 = 88.45Amps.
Then comparing this 88amps to the total 300 amp supply. There appears to be large amounts of room for expansion and the site is no where near to overloading the supply.
Have I gone down the correct route here or am i completely wrong? is there a better way to do this?
Cheers
I have done some working out but I'm not sure if I am going down the right lines, as this is not my area of expertise.
The site has a main fused switch disconnector on the main incoming supply, rated at 315amp. This then feeds a 300amp isolator, which provides power to the busbar chamber, where all the various DB's are fed from.
I have received usage data from the energy supplier. They have provided data from the previous 9 months. I have chosen the month with the highest usage. This was 13347.7kwh. This was over a 30 day period. I have then taken this value and divided it by the usage time over that 30 day period.
The site was running for 22 days out of 30, and for 10 hours a day. This gives me 220 hours running time. Therefore, I should have a kw value of 60.67kw (13346.7/220).
I have then used the 3 phase power formula, P=root3 x VL x I x Cos(theta), to find I. I have used a line voltage of 440 and an estimated power factor of 0.9.
I = 60.67kw/root3 x 440 x 0.9 = 88.45Amps.
Then comparing this 88amps to the total 300 amp supply. There appears to be large amounts of room for expansion and the site is no where near to overloading the supply.
Have I gone down the correct route here or am i completely wrong? is there a better way to do this?
Cheers