How to carry out PEFC and PSCC on a three phase db with a rcd as the supply? | on ElectriciansForums
Discuss How to carry out PEFC and PSCC on a three phase db with a rcd as the supply? in the UK Electrical Forum area at ElectriciansForums.net
RyanF
Newcastle Upon Tyne
Ive got my am2 resit tommorow for my live testing and I ran out of time and failed as well as I carried out the ze test on 2 lead high thus tripping the rcd.
So now I know for next time to complete this on a 3 lead LOW test and measure ze with earth disconnected etc.. then connect main earth back after the test.
But how would you measure pefc and pscc on the three phase db.
The plan I had was for PEFC:-
Set the megger mft1740 to L-PE on 3 low test and croc on to the main earth first, then probe on the Neutral then the phase.
So I would do :- L1- N- E
L2- N -E
L3 -N-E
Note down the highest value for PEFC.
Then same connections set the tester to L-L/L-N to measure PSCC
Same test points again
L1-N-E
L2-N-E
L3-N-E
Note down the highest value as PSCC.
If meter can measure phase to phase then do the tests. But, if not simply take the highest value and times by 2 or more accurately 1.732.
Then record this value as PFC.
Is this right or should I be doing 2 lead low test, but wont this trip the rcd? I have in my mind to do 3 lead low test to not cause any imbalance in the rcd.
Cheers!
What test meter will you be using? Have you Googled the user guide for the test meter?
On a TT system PEFC won't be the PFC. Only PSCC is relevant, and it is the maximum value between phases that you need (or double the highest phase to neutral value).
Technically a phase to phase to phase fault (i.e. a simultaneous fault between all three phases) will be the worst but we can't measure this.
Probably too late, so good luck in the test.
You know from the design of the test bay that you have an RCD in circuit at all times and you do not want to trip this therefore whenever you are measuring Zs, Ze, PEFC then use the 3 lead Lo test setting.
For the testing you have access to all conductors and so there is no need to attempt any other method of testing when testing to earth.
You should not need the green lead to earth for the PSCC test, because of the test conditions you should only test between neutral and each phase as it is not considered necessary to test between phases, the highest measured result is multiplied by 2 to give the value to record on the test sheet as PSCC.
Yep,i think we sometimes forget,that the test set-up,is different,from most of the actual real test situations,which is a bit disheartening.
That said,an understanding of the testing procedure,means the candidate should not be troubled by this.
I mean,Ze/Zb...potato/tomato...
I reckon we should go back to the days when,for example,you did military basic training,and there was an accepted percentage of fatalities...;)
Reply to How to carry out PEFC and PSCC on a three phase db with a rcd as the supply? in the UK Electrical Forum area at ElectriciansForums.net
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
Had this before, found by the DNO to be a corroded fuse carrier on a pole mounted fuse on their LV network