newbie111

just wondering how i would certify this type of installation, would i take the highest resistance value of r1+r2 of the lighting circuit and use this to add to ze? would i also have seperate values for the two circuits recorded on the EIC. any help eould be very welcome:confused:
 
Hi Newbie

I would record the lighting circuit separately on the EIC but make it clear that it is a spur off the ring main. The lighting circuit has its own protective device and Ze for the lighting circuit will be measured at the fused spur.

Cheers

Mark.
 
thanks for your prompt reply, so the fuse will be the protective device for the lighting spur and not the mcb at the distribution board? so the lighting circuit is tested as a completely seperate circuit and recorded assuch. thanks again:confused:
also if the ring trips and the lights also go out.As they are feed from the ring,does it comply to 17th as we must minimise inconvinence to users?
 
Last edited by a moderator:
Well you answered your own question, it's not a great design to take a lighting circuit of a ring final circuit, which is why you don't often see it. There is nothing in the regs to stop you doing it, as whoever did it thought that was the best design for the circumstances, and who can say he/she was wrong, as we don't know what the circumstances were.
 
where would i find the zs for a 3amp fuse,if that is the protective device and would i do pfc and pefc at that point too,thanks again.
 
Hi Newbie

I would record the lighting circuit separately on the EIC but make it clear that it is a spur off the ring main. The lighting circuit has its own protective device and Ze for the lighting circuit will be measured at the fused spur.

Cheers

Mark.

The Ze is ONLY measured at the Supply. A Zs figure should be measured at the furthest point of the lighting circuit to ensure it meets the tabulated values for the MCB.
 
so the circuit would be measured for zs at the furthest lighting point and should not be done seperately for the ring final and lighting circuit,sorry getting a bit confused on how i should complete an EIC with this circuit?:confused:
 
do the test as usuall!!

include the spur as part of the ring! as effectively thats what it is..! go to th furthest light and get a zs..! if your ZS is Higher that the ring ZS note that one down! but make sure the cert is naoted that its a socket / light circuit!
 
creating a new circuit with in a circuit on its own protective device as well!! ermmmm!! wtf! surely at some point ALL the circuits will be on a 32 unless its a magic FCU that stays on when the MCB trips!
 
I have started to record spurs with an "a" after the circuit number with the details of the fuse in the fcu as the over current device, so if the ring is on circuit 3, the spur will be 3a, I just think that anyone looking at it later when trying to sort out a problem will then know there is an fcu controling " outside lights" as an example.

May be a bit ott but not a lot of extra work.
 
just trying to get this correct( which for my small brain is something), zs is taken from the furthest lighting point and is the zs for the ring final and lights combined. The 5amp fused spur which feeds the lights will have a zs value for the fuse disconection time and this will be recorded on a seperate line and noted as a spur.
The recorded value(R1+R2 )for the lights is 1.27 ohms at the furthest point,but this is to high for a type b 32 A circuit breaker i believe. So the lighting circuit needs to be re-routed or cable csa increased?
Also the installation is a TNS, the main earth connection to the MET is 10 mm,but then has been increased to 16 mm from the met to the consumer unit. Is that acceptable? thanks in advance
 
Last edited by a moderator:

Reply to How to certify a ring main with lighting circuit taken of a fused spur??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
520
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
460

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
706
If it's going to be an emergency stop and not just a stop, then other factors come into play depending on what sort of machines the emergency stop...
Replies
11
Views
973

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top