I am having problems with understanding the regs under the PIR (Condition report inspection schedule) I have two questions:
Number one: in the section 6 regarding Shower there is a shower but the whole installation (Practice board) is not in a bathroom!! How do i fill this in as the practice board ( i.e. the installation) has a shower but there is no bathroom?If you are testing a circuit which finishes in a bath/shower room then you have to fill in the appropriate section
Number two: Section 5, regarding Final circuits the part that states Concealed cables in cooperating armour or sheath Sec. (5.11) I have a SWA as service cable, but all the erection methods for all the circuits are type B (i.e. Concealed in the practice board) what goes in the box? Is it A tick? This only applies to cables which are buried @<50mm and require either an earthed sheath or 30ma RCD protection and applies if your method is earthed sheath,your service cable is unlikely to be concealed and so it would be N/A unless you are relying on an earthed sheath for buried cables elsewhere.