How to "insulation resistance test" procedure???? | on ElectriciansForums
Discuss How to "insulation resistance test" procedure???? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
South Yorkshire
hey, could some explain how to do an insulation test, to niceic Test standards, of how you should do it when YOUR being assesed. correct procedures, aimed at those whos just done it and passed ;) cheers
If you have done a cu change they will normally ask you to IR the immersion circuit as it's less time consuming.
Ask if the assessor wants it doing at the cu or from a socket.
Isolate circuit.
Remove all lamps/neons/heating elements/dimmers/trannies from circuit (explain why you are doing this or wait for him/her to ask the question) at this point I ask if they want the test undertaken line & neutral joined then tested to cpc or as per the full test (they always ask for the full test).
Test at 500v dc between neutral & line
Test at 500v dc line - cpc
Test at 500v dc neutral to cpc
(results will be checked against cert you've issued)
At this point you'll be asked if you think the results are ok & what the minimum allowable by 7671 is & possibly at what voltage elv equipment would be tested at.
Reconnect all terminations re-energise jobs done.
set your meter to M ohms select 1000 v d.c. place one croc clip on nic mans right -------- and one on his left get your camera out and take a pic of his face as you press the test button:eek: value to record on cert,OUCH:D
set your meter to m ohms select 1000 v d.c. Place one croc clip on nic mans right -------- and one on his left get your camera out and take a pic of his face as you press the test button:eek: Value to record on cert,ouch:d
and before anybody else says it .yes im talking bo--ocks;)
anyone like to added to easyfox's mature comment, unlike paul M's....
are you allowed to do it just from the meter tails on a new installation ? or do you have to do each circuit L - N, L - cpc, n - cpc ?
or can you do it from the main breaker and test the whole lot ?
also do you have to test each lighting circuit open and closed, or just doing it all closed ok ?
can add in there the stuff which your not allowed to do, but people still do it, making u fail?
:eek:im sorry sir i thought you was allowed to have a laugh on here:eek:
You'll normally be asked to perform the test on one circuit for an assessment, it's just to show you know how to do the test & understand the results you get.
Nothing wrong with testing IR on a new installation (or for pir's) across the tails but be aware of potential low results due to parrallel circuits on larger installations.
Lighting circuits should be tested with switches on & while operating all 2 way switching in both positions (thats the one that gets forgotten).
So you can see why the assessors tend to plumb for the IR testing on immersion radials, also tests to make sure you remove the element load or neon in the DP switch ;).
Stuff you'll fail or get marked down on:
Not isolating the cu before opening/removing cover
Not removing dimmers/lamps & the likes
Not testing at the correct voltage (500v for lv or 250v elv)
Not having a calbrated tester
so if they ask for line and neutral together is that both wires between the teeth of the croc clips at the consumer and test to cpc. is it just the ins test that they dont like you disconnecting the cpc or is it for all tests?
rich
rich
I'd be surprised if they ask you to join line & neutral for this test.
But if they do; put line & neutral in one croc clip & the cpc in the other croc clip, then push the test button.
(you may be asked why this is an advantagous way to IR test some circuits & what does linking L & N achive)
You can dissconnect any cpc you like when testing just remember to re insert it prior to re-energising.
NOW CALM DOWN
Think logical, go as slow/fast as you feel comfortable with while testing, dont try to bull**** the bloke & remember to ask questions & the time will fly by.
to recap how the steps goes, when not being assessed
step 1. safty isolate the supply
step 2. Remove all lamps/neons/heating elements/dimmers/trannies and anything vunerable from circuit
step 3. set insulation resistance tester to 500v
step 4. set instruemnt to 200Mohms if it is not self ranging
step 5. test between Line and neutral (note result)
step 6. test between line and cpc (note result)
step 7. test between neutral and cpc (note result)
step 8. reconnect all terminals correctly
........ anything else??? anything wrong???
Testing the circuits individually
lets say that test above is for testing from the tails, so when doing it individually do you have to remove the cpc and neutral, use a croc clip for them and use the probe onto the breaker?
can the test be done, having the supply isolated, all breakers on. and testing by using the probes onto the earth bar & neutral bar.
neutral bar & isolated side of the main breaker? is this ok?
thankyou in advanced, please quote where i've gone wrong ;) cheers
no one like to add...?
Reply to How to "insulation resistance test" procedure???? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...