Currently quoting for a job that needs to be done next week and working out how best to proceed, so thoughts welcome.
Current situation:
-->PME incomer that has just been moved by UKPN within a porch (brick built permanent type) from one wall to another.
-->60A main fuse
-->Meter
-->Large MK metal isolator on same board that is so old it's back in fashion...
-->16mm Twin and Earth which runs up and through the ceiling of the downstairs toilet (about 4-5m length) to the existing CU, which is a metal AMD 3 board, with dual RCD and apparently has a certificate.
Because of the move, the 16mm twin and earth no longer reaches the isolator properly, so currently dangling through air across the porch.
Client wanted power and light in the new larger porch and the 16mm feed extended.
My solution is currently to install a new small CU in the porch, which will contain RCBOs for the 2 local circuits, then connect the 16mm feed into this as a submain on a 63A breaker.
Bonding of Gas and Water has been run to the incomer earth terminal fortunately, so don't need to worry about the submain sizing for that. I haven't done the adiabatic yet, but I think it will comply for fault current - although the Ze was low at 0.1.
I'm planning to install a fusebox CU with SPD included, which will then upgrade the entire installation so seems the best method in the circumstances.
The issue is that the 16mm cable currently runs through the ceiling of a downstairs toilet, with bathroom above. Neither are accessible (bathroom tiled, ceiling plastered), so it is impossible to verify whether the cable is >50mm deep from both. It does not appear to run through any walls at least.
Installing an RCBO as protection for the submain clearly causes discrimination issues.
If I was running it all as a new install, I would likely run the sub main in armoured, or at least ensure that it was >50mm, but it's likely been like this since the property was built (70s I believe)
Any thoughts on my current solution or other options that I'm missing?
Current situation:
-->PME incomer that has just been moved by UKPN within a porch (brick built permanent type) from one wall to another.
-->60A main fuse
-->Meter
-->Large MK metal isolator on same board that is so old it's back in fashion...
-->16mm Twin and Earth which runs up and through the ceiling of the downstairs toilet (about 4-5m length) to the existing CU, which is a metal AMD 3 board, with dual RCD and apparently has a certificate.
Because of the move, the 16mm twin and earth no longer reaches the isolator properly, so currently dangling through air across the porch.
Client wanted power and light in the new larger porch and the 16mm feed extended.
My solution is currently to install a new small CU in the porch, which will contain RCBOs for the 2 local circuits, then connect the 16mm feed into this as a submain on a 63A breaker.
Bonding of Gas and Water has been run to the incomer earth terminal fortunately, so don't need to worry about the submain sizing for that. I haven't done the adiabatic yet, but I think it will comply for fault current - although the Ze was low at 0.1.
I'm planning to install a fusebox CU with SPD included, which will then upgrade the entire installation so seems the best method in the circumstances.
The issue is that the 16mm cable currently runs through the ceiling of a downstairs toilet, with bathroom above. Neither are accessible (bathroom tiled, ceiling plastered), so it is impossible to verify whether the cable is >50mm deep from both. It does not appear to run through any walls at least.
Installing an RCBO as protection for the submain clearly causes discrimination issues.
If I was running it all as a new install, I would likely run the sub main in armoured, or at least ensure that it was >50mm, but it's likely been like this since the property was built (70s I believe)
Any thoughts on my current solution or other options that I'm missing?