Hi All , How do i size the main , star and delta contactors for a motor control circuit using a 50Kw motor ? Do i just rate all contactors at 50 kW ?

Any help appreciated.

Thanks :)
 
at a guess size the main for the the FLA ac3 rating

the star and delta contactor maybe 60% FLA ac3 or more

the overload can go in any of 3 places for star/delta in theory
 
Last edited by a moderator:
that should be 35,60,100% for star delta and main

the main contactor makes in star but breaks FLA

can't recall if they're sized that way in practice-i assume so

the overload in series with the motor windings gives the closest protection folowed by supply lines and delta
 
Hi All , How do i size the main , star and delta contactors for a motor control circuit using a 50Kw motor ? Do i just rate all contactors at 50 kW ?

Any help appreciated.

Thanks :)

Hi there,
Main = IFL x 0.58 - if your main contactor is in phase, else IFL.
Delta = IFL x 0.58
Star = IFL x 0.33
Note your overload size/setting:
If your overload in in line the = IFL
If your overload is in phase then = IFL x 0.58

Just remember you are starting a motor so choose contactors at ac3 rating.

Greetings:)
 
ya the main is in phase on my drawing as well ( i misread it) so thats 35,60 and 60 appprox for star delta and main


i i supppose the 'main' may go on the lines as well if the overload is placed there so that would be 35,60 and 100 in that case
 
Last edited by a moderator:
Star Delta is an old way of doing thing now, on something this size we would use an inverter. most companies have now changed over to soft starts but the do get hot so you panel will need some ventilation/fan
 

Reply to How to 'size' contactors for star delta circuit ? in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Why are you doing this, you potentially could cause mains transients on smaller power networks and local installations, the reason it has a...
Replies
3
Views
1K
  • Question
Here are the other drawings
    • Optimistic
    • Funny
Replies
6
Views
1K
  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
842
I got this all wired in and working thanks to the help from James, absolutely top man. Do have a small issue with current imbalance atm, L3...
Replies
10
Views
2K
  • Question
Yeah, I've now got all that but with the electronic timer. The ABB AF contactors aren't compatible with the Schneider SD timer, but ABB don't do a...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks