How to test a faulty ballast???? | on ElectriciansForums
Discuss How to test a faulty ballast???? in the Australia area at ElectriciansForums.net
A
a.e.s
How do I test a faulty ballast on a fluorescent light fitting?
Many thanks in advance.
In what way is it faulty?? blowing fuses/MCB or just not working.
1.I would carry out insulation test
2.Check continuity of winding (handy if you have a good one to compare results against)
Hope this Helps
Intermitten fault, its tripped the mcb twice in the last week. I dont think its the starter it happens once the lights have been on about ten hours, im just not sure which light it is there are six light fittings.
Sounds like something is getting hot then maybe the insulation is breaking down. Is there a way you could isolate a couple of fittings and leave the remainder on and see if it still trips.
If not split the circuit out and test each fitting comparing the results of each.
Rgds
G
If the power factor correction capacitor is breaking down (slight smell of burning) then too much current will be drawn and this increased current could trip the thermal part of the mcb after a few hours.
Get the insulation resistance tester out. These things sometimes work until they get hot as an earlier poster stated.
In a factory I used to do maintenance for there was an RCD covering several lights with magnetic ballasts and occasionally one of them would cause tripping. Testing live or neutral to earth usually pinpointed the culprit.
You could fit high frequency ballast(s) but those babies leak current to earth anyway (or they don't work) so be careful how many you use on an RCD :)
Reply to How to test a faulty ballast???? in the Australia area at ElectriciansForums.net
You really need an inductance or LCR meter or a ring tester which are expensive to buy but you can make your own ring tester if you want a project...
At this "first" fitting it's loop in. The rest appear to be joint boxes and old par 38 light fittings. It is reasonably old wiring but not...