How to wire Hager CDA263U RCD? | on ElectriciansForums
Discuss How to wire Hager CDA263U RCD? in the DIY Electrical Advice area at ElectriciansForums.net
Mill
Can I connect the supply line and neutral to the terminals 2&4 and the load side line and neutral out of terminals 1&2[ElectriciansForums.net] How to wire Hager CDA263U RCD?
It clearly shows the supply into 1 and 3, 1 would be the live.
This has cropped up before on this forum, and the claim was made that Hager state they can be fed top or bottom.
So, seeking the evidence, I found the very last page of the Hager Residential Catalogue, which gives common technical characteristics for the range (If I'm interpreting this correctly), it does say it can be fed either way:
The schematic clearly shows the feed to 1 and 3 and whilst I agree inverting this may not make a difference the schematic should be adhered to.
I do agree the obvious way to connect it is as printed on the device, but it does appear acceptable to do it the other way if there was a good reason?
What must not be done is to feed live from the top on one side and neutral from the bottom on the other, or vice versa.
The Previous RCD is wired this way , its being changed because it’s trip value is 0.3A
  • [ElectriciansForums.net] How to wire Hager CDA263U RCD?
Are you based in Southern Ireland?
Well altering a consumer unit is restricted works and legally should only be carried out by an REC.
Reply to How to wire Hager CDA263U RCD? in the DIY Electrical Advice area at ElectriciansForums.net
Any chance of a photograph? What you’re describing seems straight forward. Just because a wire is black, doesn’t instantly mean it’s a neutral...
You were correct those are neutral wires, it worked! Many thanks