Even at 100w they were well within a 6Amp Mcb, Does anyone actually fit smaller than a 6Amp for lights? There not that common are they smaller MCBs
More than 100W of LED lighting, in particular simultaneously-switched, is very unusual for a home. Maybe if you have a 5-a-side pitch outside and want floodlights for dark evenings...
Most consumer boards only have matching MCB down to 6A, a couple of brands offer 1A or 2A, but often you need to look at the industrial type of three-phase boards, etc, to get a wide range of small currents. Hager, for example, go down to a 0.5A C-curve MCB.
But as with a lot of electrician's work, the majority of installations fall inside the "typical" cases and for that you can look up the on-site guide table 7.1 and if your setup falls within the typical cases of 6A lights / 20A radial / 32A ring then no fancy maths needed at all.
And the typical sizes are pretty generous. For example, even with 1mm T&E on a 6A B-curve MCB you have 68m length. Quite a size for a single circuit to cover!
Going by the above LED example and working backwards, allowing x6 for the surge factor that is 1A steady-state, and then you are looking at 230W of lights (around 1.5kW in tungsten lamp brightness terms)
simultaneously-switched. You can probably increase by a factor of 2-3 for a typical home or small office setup as most rooms won't have more than a half dozen on the one switch.
As most LED lamps are under 15W, that is over 15 outlets per switch, subject to maybe 30-45 total. Again, a lot for the area a typical single circuit would cover.
But the reason you have to do these questions in gaining your qualifications is not for day-to-day work, but to demonstrate you have a grasp of the electrical principles for the odd case where you have an unusual set up that falls outside of the norm.