Just thought I would start some posts for some of the less experienced lads on here, and for guys who are predominately domestic.

Here is the start of what is going to be a 3 story building. Grd floor workshops and tech area 1st floor will be classrooms and briefing areas and offices final floor offices, conference room, etc


[ElectriciansForums.net] How we Earth here

Because of the system here we do get our protective earth from the supply transfomer which is going to be installed during this build. Which was sized as 700KVA

[ElectriciansForums.net] How we Earth here[ElectriciansForums.net] How we Earth here

Above though is going to be part of the earthing system as well, but will be more functional earthing. This will be tied in with earth pits and will form a 1ohm requirement for IT. This is the famous ufer earthing system which I think as been covered on here and will when tied in with the pits will give me less than the required 1 ohm

[ElectriciansForums.net] How we Earth here

This is the result. I have 4 x 95mm conductors on each of the 4 corners of the building and we start from there

If people are interested I'll post over the coming months, the TX installation, to the building being built and various stages of the installation till completion .

This though is just 1 of 6 new builds I have and 14 refurbs lol
 
I normally try and drive a rod in every 7-9mtrs around the Building. I use 1800mm x 19mm rods so I'm guessing with the buildings foot print we will have about 17-18 rods in total. All the rods will be linked with a 70mm bare conductor laid in earth.

Theses will also tie in with the lightning system so I will be looking at a result of 0.5 ohms or less to be honest Lee.

I have stopped us using Furse, no reflection on furse, it is good stuff, but compared to Wallis it's twice the price and that is bringing Wallis from the UK

In the scheme of things I'm guessing the system will be 3-4K UK
 
Last edited:
I normally try and drive a rod in every 7-9mtrs around the Building. I use 1800mm x 19mm rods so I'm guessing with the buildings foot print we will have about 17-18 rods in total. All the rods will be linked with a 70mm bare conductor laid in earth.

Theses will also tie in with the lightning system so I will be looking at a result of 0.5 ohms or less to be honest Lee.

I have stopped us using Furse, no reflection on furse, it is good stuff, but compared to Wallis it's twice the price and that is bringing Wallis from the UK

In the scheme of things I'm guessing the system will be 3-4K UK

Other than the price of their kit, used Wallis stuff for many years because Furse seem to charge for their name when buying their kit
 
The Attached Pdf is Malcoms donation to the thread, but he was having issues with the system so thank him not me for this please guys.
 

Attachments

  • Sch [7852].pdf
    108.9 KB · Views: 76
Last edited:
I normally try and drive a rod in every 7-9mtrs around the Building. I use 1800mm x 19mm rods so I'm guessing with the buildings foot print we will have about 17-18 rods in total. All the rods will be linked with a 70mm bare conductor laid in earth.

Theses will also tie in with the lightning system so I will be looking at a result of 0.5 ohms or less to be honest Lee.

I have stopped us using Furse, no reflection on furse, it is good stuff, but compared to Wallis it's twice the price and that is bringing Wallis from the UK

In the scheme of things I'm guessing the system will be 3-4K UK
What sort of readings are you getting from the rebar once the concrete has been poured?

I always find it to be hit and miss a job I did recently was getting readings of under 0.10 ohms but on another job similar sized concrete slab was over 700 ohms. Probably just down to the quality of the rebar ties or something I'd imagine but curious nonetheless.
 
What sort of readings are you getting from the rebar once the concrete has been poured?

I always find it to be hit and miss a job I did recently was getting readings of under 0.10 ohms but on another job similar sized concrete slab was over 700 ohms. Probably just down to the quality of the rebar ties or something I'd imagine but curious nonetheless.

You would probably find rather than the steel ree bar being the culprit, that it is the concrete itself that is giving you the poor results.

I've seen literally a piece of ree bar pushed in a concrete pour and once it formed that was used as the earth rod and results were pretty good, I can't remeber the exact results but it was less than 10 ohms

Your 700 ohms is surprising though.
 
The Attached Pdf is Malcoms donation to the thread, but he was having issues with the system so thank him not me for this please guys.

Thanks Glen.

I posted this mainly for the trainees and perhaps guys that are just getting into design. It's a doc I developed out here that we submit to the clients O+M office for approval.

You can see, hopefully how we go about doing the intial design and I'm sure it can be altered, or changed to suit. Notice I haven't put R1 + R2 on it, here that would totally confuse things lol. Back in the UK youd could add a column for that

Just hope it might help someone
 

Reply to How we Earth here in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
928
  • Question
Hello Dave, Thanks for taking the time to reply. I appreciate the info, I haven't updated this post yet, but I have since been talking to some...
Replies
3
Views
1K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Thread Information

Title
How we Earth here
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Thread Tags

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top