Octopus
OK.
Doing an EICR on a "chapel" in the middle of a grave yard today.....
So there is a 40A MCB, with 6mm T&E running through the wall to:
Then the 3 x 2.5 mm's each run in surface trunking (the longest run is about 10m) to 1G 13A sockets and at each one there is a wall mounted 3KW fan heater plugged in.
Now I am a bit torn between a C3 and a C2 for the cable/OCPD
and for the plugs for the heaters I'm inclined to give a C3 with a recommendation that they plug and socket be replaced with a S FCU.
So how would you guys view this install?
AND
They reported issues with the 32A MCB tripping - I looked hard to see what it did but apparently nothing BUT with it disconnected from the MCB is showing:
It transpired that one end of the ring was in the adjacent 20A MCB and this is the other end which used to be in the 32A MCB - which won't reset at all.
Also in my inspection of the property I nearly missed this socket (its how you turn on the outside light!):
You have to look hard to see it - C3?
And of course there are 2 lighting circuits, both 1.5mm T&E on 20A MCB's
And the CU is a fairly rare GEWISS board!
All in a fun days work!
Doing an EICR on a "chapel" in the middle of a grave yard today.....
So there is a 40A MCB, with 6mm T&E running through the wall to:
Then the 3 x 2.5 mm's each run in surface trunking (the longest run is about 10m) to 1G 13A sockets and at each one there is a wall mounted 3KW fan heater plugged in.
Now I am a bit torn between a C3 and a C2 for the cable/OCPD
and for the plugs for the heaters I'm inclined to give a C3 with a recommendation that they plug and socket be replaced with a S FCU.
So how would you guys view this install?
AND
They reported issues with the 32A MCB tripping - I looked hard to see what it did but apparently nothing BUT with it disconnected from the MCB is showing:
It transpired that one end of the ring was in the adjacent 20A MCB and this is the other end which used to be in the 32A MCB - which won't reset at all.
Also in my inspection of the property I nearly missed this socket (its how you turn on the outside light!):
You have to look hard to see it - C3?
And of course there are 2 lighting circuits, both 1.5mm T&E on 20A MCB's
And the CU is a fairly rare GEWISS board!
All in a fun days work!