Depends where they are buried?? In area's subject to the presence of the general public, such as footpaths walkways etc, anywhere around 0.75+m was the old electric boards standard depth. Deeper if in agriculture settings where for example fields were subject to mechanically farrowing/plowing etc
 
thanks e54 would have thought it would of been deeper than 0.75m dosnt seem deeper enough

- - - Updated - - -

thought i seen or read somewere that it had to be 3m but ill trust your judgement
 
thought i seen or read somewere that it had to be 3m but ill trust your judgement..

deeper than that if you want to stay out of the way of E54's earth rods.
:95:
 
GN 1 Table 5.2 guidance for recommended buried cable depth:- HV cables buried under footway/verge 400-600mm and carriageway 750mm, EHV cables buried under footway/verge or carriageway 750-1200mm.
 
GN 1 Table 5.2 guidance for recommended buried cable depth:- HV cables buried under footway/verge 400-600mm and carriageway 750mm, EHV cables buried under footway/verge or carriageway 750-1200mm.

Just goes to show the laxing off of the older standards. That figure you have shown, used to be (as near as dammit) for ducted networks under public footpaths and walkways etc!! I wonder if they even bother with ducting systems now!! ...lol!!
 
thought i seen or read somewere that it had to be 3m but ill trust your judgement..

deeper than that if you want to stay out of the way of E54's earth rods.
:95:

Why, .....no-one seems to bother past a single earth rod or twig in the UK these days!! :angel_smile::6:
 
It’ll take more than a copper rod to stop me biting you when I’m dead.

Solid gold or if you’re a cheapskate a straight bough of Yew driven through the heart when I'm buried face down.
 

Reply to hv cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
185
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
pretty sure from memory they are indeed designed to work on both frequency's, Best check with Schneider but I think they will work on 60 HZ
Replies
4
Views
718
  • Question
Hi Swirl, Yes I have been a LV AP and am also a HV AP, to become an AP you need to start to create a AP log book, inside you supply your...
Replies
1
Views
490

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top