Just been asked to quote for work in a church required by a PIR undertaken by another NICEIC electrician.
He's given a code 1 (really?) to no RCD protection (doesn't specify for what).
The church has PME earthing and two 3ph boards - one supplies storage heating, the other lighting, a few sockets and some overhead heaters. I have suggested that RCD protection should be put in for sockets which might be used for portable equipment outdoors (code 2 according to the Best Practice Guide No.4 Periodic Inspection Reporting by the ESC).
Presumably, I have to get the churchwarden to question the recommendations and get an amended PIR if they can't be justified?
Pete
He's given a code 1 (really?) to no RCD protection (doesn't specify for what).
The church has PME earthing and two 3ph boards - one supplies storage heating, the other lighting, a few sockets and some overhead heaters. I have suggested that RCD protection should be put in for sockets which might be used for portable equipment outdoors (code 2 according to the Best Practice Guide No.4 Periodic Inspection Reporting by the ESC).