1. What do I put in the cpc size on the test schedule if the steel trunking and conduit is used as cpc?

2. same as above but for swa strands used as cpc?

3. how do I do zs at a 3 phase circuit with no neutral. My meter usually needs neutral to get zs measurment? (Unitest Telaris 0100 plus)
 
1. What do I put in the cpc size on the test schedule if the steel trunking and conduit is used as cpc?

2. same as above but for swa strands used as cpc?

3. how do I do zs at a 3 phase circuit with no neutral. My meter usually needs neutral to get zs measurment? (Unitest Telaris 0100 plus)


The NIC have a few accepted abbreviations for containment used as cpc..... 1. Trun, 2. Con, 3. SWA & 4. MICC.

Generally these should suffice regardless of what flavour of test form you use.

If you're sure your meter cant directly measure Zs, you can calculate if from Ze+(R1+R2).
 
I've never used the meter but can't you do a PSCC (Ri for that meter I think?) but connect L to Line and N to cpc?
The instrument shouldn't care that it is measuring Line to earth loop instead of the expected Line to neutral.

Like I say, I don't know your instrument so take this with a pinch of salt..........

RCDs will not like it of course if you have them!
 
Amtech does mine for me :):) drop down has trunking then a wee box asking size hey presto actual size in the cert
same for SWA,conduit altho not light gauge/heavy gauge conduit
 

Reply to I have a few questions concerning the EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top