Goody

-
Joined
Jan 21, 2010
Messages
638
Reaction score
94
Location
London
  1. I am testing “Voltage Drop” at the mini DB where the SWA cable from the main DB terminates into and I am not seeing much of a difference between Voltage readings at the mini & main DB’s. The cable run is around 40 ft. Could I use the test lead with 3 pin plug on my Fluke 1652 on live sockets at the garage and at the house to check the voltage (with some load on the circuits)? What is the best way to get an accurate reading of voltage drop? Also, because this lead has no fuse in it (not sure if it does), would I damage the meter?
  2. I have a mirror light with integrated 2 pin shaver socket (SELV). What tests I do on it and how do I go about doing them? Many thanks!
3 pin plug on my Fluke 1652 -> [ElectriciansForums.net] I have two questions.
 
If you test the voltage at the mini board with no load connected you will get very little if any volt drop reading
When a load is applied thats when it would become evident
 
If you test the voltage at the mini board with no load connected you will get very little if any volt drop reading
When a load is applied thats when it would become evident

And the load applied would need to be your full design current in order to get an accurate reading.

Just calculate it as widdler said (which you should have already done when designing the circuit). :hand:
 
Thanks, folks. I have not designed this circuit but it was already in place and I have done a CU change as part of assessment; I needed to find this out for the record. The R1+R2 = 0.57 ohms. Thanks
 
Hi,
If you are calulating voltage drop, should you not be measuring R1+Rn, and then looking at the design current and then the tables in the BRB and calculating (mV/A/M)/1000 ?
 
Last edited:
Hi,
If you are calulating voltage drop, should you not be measuring R1+Rn, and then looking at the design current and then the tables in the BRB and calculating mV/A/M ?

You're only using continuity results to determine the length of the cable run. This can be done using R1 + R2 results and dividing by the resistance per meter from Table 9A OSG for whatever size the line and cpc are.
 
Last edited by a moderator:
Hi Jud,
yes I get that bit, I suppose you could just double your R1, I was thinking more about calculating the volts drop on T+E, where your CPC can be smaller, or if the armour of an armoured cable was used as a cpc.

Trying to learn for my 2391 :28:
 
Last edited:
Hi Jud,
yes I get that bit, I suppose you could just double your R1, I was thinking more about calculating the volts drop on T+E, where your CPC can be smaller, or if the armour of an armoured cable was used as a cpc.

Table 9A gives you the resistance per meter for cables with smaller cpcs -- eg. 2.5mm² + 1.5mm² = 19.51mΩ/meter (2.5mm² = 7.41mΩ/meter & 1.5mm² = 12.10mΩ/meter -- 12.10 + 7.41 = 19.51mΩ/meter)

You would the divide your R1 + R2 result by 19.51 Ă· 1000 (0.01951) and that would give you the length of the cable
 
Last edited by a moderator:
What I was asking (sorry to jump on to someone elses thread), was when calculating volts drop, is do you need to double the length to take into account the return via the neutral in your (mV/A/M)/1000 calculation ?

I cannot find where the calcs are for this at the minute, I cannot see it in the BRB or GN3, it may be in unites red book
 

Reply to I have two questions. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
763
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
765

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
252
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top