This is the digram that i came up with, i am running mostly 12-2, on 20amp for everything. Except for my electric stove, i was planning 6 gauge wire on a 50a.
i am trying to wire in two three ways light switches, and was going to run 12-3 between them and 12-2 to the lights and the service panel. Does that work?
 

Attachments

  • 644229B9-26F1-4BE2-BE8D-4EEB194CA093.png
    644229B9-26F1-4BE2-BE8D-4EEB194CA093.png
    926.5 KB · Views: 57
This is the digram that i came up with, i am running mostly 12-2, on 20amp for everything. Except for my electric stove, i was planning 6 gauge wire on a 50a.
i am trying to wire in two three ways light switches, and was going to run 12-3 between them and 12-2 to the lights and the service panel. Does that work?
Yes that will work but you can use # 8 wire for your stove
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Helena, mt
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
Other
If other, please explain
Not an electrician
Business Name
Ya

Thread Information

Title
I need some help! ASAP, questions a put wire, three ways and stoves.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1
Unsolved
--

Advert

Thread statistics

Created
drool624,
Last reply from
Megawatt,
Replies
1
Views
972

Advert

Back
Top