hi someone mentioned to me that the lads he worked with did blanket testing for insulation resistance testing is this possible or do i need to tell him to do the job properly
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss I/R testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Also be warned that if you link between Phase and Neutral and test from that to earth you must note this on your report as you have not tested between Phase and Neutral, and there should be good reason to do this test and not use it because it is easier. One reason to do this type of test is if it is not possible to remove all lamps or neons.
Also be warned that if you link between Phase and Neutral and test from that to earth you must note this on your report as you have not tested between Phase and Neutral, and there should be good reason to do this test and not use it because it is easier. One reason to do this type of test is if it is not possible to remove all lamps or neons.
If you do this you still test between Phase and Neutral but only at 250V, that way the electronics dont get damaged and you have some measure of confidence but it needs to be noted.