Hi, I was wondering if anyone can explain to me how to work this out...... When taking an insulation resistance reading beteeen line and cpc, at what reading in megaohms might you expect the 30 milliamp leakage threshold to be reached that would trip the rcd? Its just a theroretical question, its not to do with any work that im on. Its just that I had a reading yesterday of around 465 megahoms testing some existing wiring. I know thats fine as the rcd was holding in ok, I was just wondering how low that reading can go before tripping will occour ? Cheers
 
R=V/I
Therefore R=230/30ma
So R = 7.67K ohms

Don't forget that most 30ma RCDs will trip at less than 30ma, also the voltage is often higher than 230v.
 
Hi, I was wondering if anyone can explain to me how to work this out...... When taking an insulation resistance reading beteeen line and cpc, at what reading in megaohms might you expect the 30 milliamp leakage threshold to be reached that would trip the rcd?


<2 Mega ohms suggests a latent fault!
 
Last edited:
Ah, so thats how you do it. So what would anyone who reads this ,their opinion be of the minimum reading you would accept in terms of megaohms so you could be reasonably sure that the rcd would not trip?
 
just to be clear, this is a theroretical question, of course the powers off, and ive carried out my safe isolation procedure, ive locked off the main switch, ive switched off my van outside the house and im wearing my trousers
 
gpz, you've got your answer. . the IR test is not to determine the trip threshold of the rcd. although it would take around 7.67.ohms to trip the rcd, the IR test is to determine the state of the insulation between conductors , including the itegrity of accessories. as malcolm says, a reading of less than 2 meg. would indicate a potential breakdown of insulation which, left , could in time decrease to a value to cause arcing between L/N/E.
 
The IR test should be done at 500V so the theoretical minimum resistance figure is 16.667 Kohms for 30mA to flow

This is 120 times lower than the recommended 2Mohm.
 

Reply to I think that this is one for ohms law in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

  • Question
It might be worth asking the customer to turn the oven on 45min before you arrive. then do an IR test on the oven from the isolator with the oven...
Replies
6
Views
1K
  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top