Hey if a motor is rated at 0.37kW and will be run in delta. and the power factor is 0.65 at a voltage of 400v in 3 phase how do you work out the running current.
is it 0.37/400??
is it 0.37/400??
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ib running current in the Australia area at ElectriciansForums.net
Hey if a motor is rated at 0.37kW and will be run in delta. and the power factor is 0.65 at a voltage of 400v in 3 phase how do you work out the running current.
is it 0.37/400??
when we used to use english terms we would use V, not U. but according to europe, V for Volt is illogical.
what does the abreitation Uo mean please?
Uo is the line voltage to earth.
However that is incorrect for your scenario.
You want UL, as it is given in syllabus, or U, as it is defined in BS7671. This is for the voltage between lines (i.e. 400v). Use it as I wrote it down earlier.
And there you have it ...........no messing around just the advice you asked for nothing more nothing less.