Hey if a motor is rated at 0.37kW and will be run in delta. and the power factor is 0.65 at a voltage of 400v in 3 phase how do you work out the running current.

is it 0.37/400??
 
Hey if a motor is rated at 0.37kW and will be run in delta. and the power factor is 0.65 at a voltage of 400v in 3 phase how do you work out the running current.

is it 0.37/400??

Remember when working out design current for 3phase the formula changes to Ib=P/(√3XUL) plus the factor needs to applied in the formula.
 
what does the abreitation Uo mean please?

Uo is the line voltage to earth.

However that is incorrect for your scenario.

You want UL, as it is given in syllabus, or U, as it is defined in BS7671. This is for the voltage between lines (i.e. 400v). Use it as I wrote it down earlier.
 
And there you have it ...........no messing around just the advice you asked for nothing more nothing less.
Uo is the line voltage to earth.

However that is incorrect for your scenario.

You want UL, as it is given in syllabus, or U, as it is defined in BS7671. This is for the voltage between lines (i.e. 400v). Use it as I wrote it down earlier.
 

Reply to Ib running current in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
228
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Hi tssxrr, I am also doing my assignment on the same topics. would you mind sharing the documents which you have done so I will have rough idea...
Replies
1
Views
2K
Yeah when we start up the cone crusher the power factor can drop from .9 to .5. I’ve seen it drop down to .4 during start up. We have more than...
Replies
5
Views
819

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top